    Plumber in the house??? Pilot light won't stay lit on WH...

    Gas supply seems to be fine...

    Anything else to check?

    The WH is only about 2.5 years old.

    Brandon
    "When you can't make them see the light, make them feel the heat." - Ronald Reagan

  2. #2
    Boolit Master Pb2au's Avatar
    Join Date
    Mar 2010
    Location
    Southwest Ohio
    Posts
    1,228
    Check for a build up soot around the orifice where the flame emanates. It may be causing the issue.

  3. #3
    Boolit Master
    farmerjim's Avatar
    Join Date
    Nov 2012
    Location
    St. Francisville, Louisiana
    Posts
    1,928
    The Thermocouple is probably bad.

  4. #4
    Boolit Buddy longranger's Avatar
    Join Date
    Jun 2009
    Location
    Buffalo WY
    Posts
    343
    Second the thermocouple. HW heater should still be under warranty no ?

  5. #5
    Boolit Buddy BBQJOE's Avatar
    Join Date
    Mar 2013
    Location
    I challenge your middle of nowhere, and raise you 5.
    Posts
    433
    Does the pilot light burn? If not, try heating the thermocouple with a match or torch in the pilot position. Then turn it to on. If the burner lights, it's not the thermocouple.
    I have seen where the gas feed to the thermocouple sometimes seems to plug up with some junk that can't be poked out.
    Guns should only be allowed in places where people don't want to be shot.

  6. #6
    Boolit Master Sprue's Avatar
    Join Date
    Apr 2007
    Location
    WV
    Posts
    840
    ...had the same issues a while back. I found a brass brush that resembles a toothbrush. I then taped it onto a wood dowel rod to lengthen it. Gently run the brush all around the igniter & thermocouple. If you take a strong flashlight and look in that area, you will probably see a "white" buildup of deposits. Mine has worked ever since.

    Good Luck
    Sprue ™

  7. #7
    Boolit Master mroliver77's Avatar
    Join Date
    Mar 2005
    Location
    Northwest, Ohio
    Posts
    2,922
    I thought all new gas appliances were electronic ignition. No standing pilot.
    J
    "The .30-06 is never a mistake." Townsend Whelen

    "THESE are the times that try men's souls. The summer soldier and the sunshine patriot will, in this crisis, shrink from the service of their country; but he that stands by it now, deserves the love and thanks of man and woman. Tyranny, like hell, is not easily conquered; yet we have this consolation with us, that the harder the conflict, the more glorious the triumph."
    Thomas Paine

  8. #8
    Boolit Buddy

    Join Date
    May 2013
    Location
    michigan
    Posts
    408
    Clean the thermocouple of any soot and then inspect it. If it appears to be melted or burned through in any spot, replace it. Ensure that the coil does not touch any metal part between the tip and the threaded base.
    Thermocouples generate a small electric current when heated, that electric current hold open the gas solenoid valve.

    While you are at it, drain about 5 gallons of water from the drain valve on the heater.

  9. #9
    Boolit Buddy
    Join Date
    Jul 2013
    Location
    Summerville Ga
    Posts
    157
    Replace the thermocouple, cost is around $7 or less. Even if your thermocouple looks fine, still replace it. 99% ot the time this is the issue.

    Robert

  10. #10
    Boolit Master

    Sweetpea's Avatar
    Join Date
    Jun 2012
    Location
    Southern Utah
    Posts
    1,313
    OK...

    So I found a new thermocouple, newer style with 2 wires, cost $28 something.

    Hooked it up, and no dice.

    There is flame when you light the pilot, but the pilot will not stay lit.

    I really would like a warm shower today...
    "When you can't make them see the light, make them feel the heat." - Ronald Reagan

  11. #11
    Moldy Boolit Phoenix's Avatar
    Join Date
    Jan 2013
    Location
    BFE, Arizona
    Posts
    292
    Quote Originally Posted by mroliver77 View Post
    I thought all new gas appliances were electronic ignition. No standing pilot.
    J
    All my gas appliances are less than 2 years old and they all have pilots, brand new Bosch tankless hot water heater brand new range from Ge

  12. #12
    Moldy Boolit Phoenix's Avatar
    Join Date
    Jan 2013
    Location
    BFE, Arizona
    Posts
    292
    If the flame from the pilot is hitting the thermocouple and you change the thermocouple then the only other thing it can be if it won't stay lit is the control valve.

    If the flame is not hitting the thermocouple then your problem is probably related to the flame not being big enough or strong enough to reach it. Clean the air inlet most of the time there's a small screen around it can get plugged with dust usually just some compressed air is enough to solve the problem

  13. #13
    Boolit Master daniel lawecki's Avatar
    Join Date
    May 2012
    Location
    toledo ohio
    Posts
    722
    Is it a Whirlpool pre bent thermocouple because the price of the part tells me so pm me.

  14. #14
    Boolit Master
    turmech's Avatar
    Join Date
    Jan 2012
    Location
    Delmarva
    Posts
    533
    Look for a reset button. Many newer water heaters have have them. In the pic it is to the right and white in color. In the center is a push button. Most of the time there is a slight audible click or you feel it click. You also should have continuity through the switch with the wires off if you have a ohm meter.

    If that is the problem you need to check the flame of the main burner and make sure it is flowing up and out of the water heater. If it is rolling out sideways you have a problem in the venting.

    You may want to move the water heaters temp setting as some times they stick and overheat the switch. If all that is OK the switches do go bad.
    Attached Thumbnails Attached Thumbnails water heater limit.jpg  

  15. #15
    Moderator Emeritus


    Join Date
    Mar 2005
    Location
    SW Montana
    Posts
    12,496
    The flame should envelope the thermocouple, as in surround the top 1/3-1/4 of it. The flame should be near blue and not soft and waveing like a candle flame. If the flame does not make sure that the t-couple is pushed in all the way forward. The quickest fix for a dirty pilot is to tap the pilot assembly with the end of a screwdriver. If there is a porcelain ignitor do not hit that. make sure the gas is flowing through the pilot when you do this by holding the pilot valve in so it carries away any dust or crud. I have not seen a 2 wire system on a WH but have been out of the service end for a few years. A screw in t/couple has a millivolt raring of 30 mv and 12-15 should be enough to hold the pilot safety in. A quick check with a volt meter will confirm this. Gas valves do go bad but it is rare. WH warranties were 5 yrs on tank and one year on the components for a long time. That leaves you out of luck @ 2.5 years.
    If you have a barbeque lighter heat the thermocouple tip as the pilot is lit for no more than 30 seconds and check to see if it stays lit. If it does there is not enough heat to keep things lit. If not it is probably a valve issue with a new thermocouple. There may be a red reset button on a rollout switch. If there is too much heat that would indicate a venting failure and the system would lock out. Some are manually resetable others are a one time use. All of these components and connections eat voltage and you have only 30/1000 of a volt to work with. In the good old days a gas valve was 50% of the cost of a WH. I have no idea what they run now. In either case to drain the WH, replace the valve and check the system ran about 1 hr labor or almost the same as replacing the heater. AS a young hot shot if you were lucky you could stab a new one while the water was still on while pulling the old one with out loosing over a gallon of water if the shut off valves were shot. A 2 1/2 yr old WH might be new enough to take the risk of replacing it.
    I am sending you my phone # by PM if I can help. Good luck with it.
    [The Montana Gianni] Front sight and squeeze

  16. #16
    Banned
    Join Date
    Nov 2012
    Location
    Central Virginia
    Posts
    7,439
    Quote Originally Posted by longranger View Post
    Second the thermocouple. HW heater should still be under warranty no ?
    + 3 or more on the bad thermocouple

  17. #17
    Banned



    Join Date
    Jan 2011
    Location
    Color Me Gone
    Posts
    8,401
    The valve on mine won't stay rotated in right place, so I had to duct-tape it into place. Just fully rotated it and applied the tape. Definite Beer Can Engineering.

  18. #18
    Boolit Master

    Sweetpea's Avatar
    Join Date
    Jun 2012
    Location
    Southern Utah
    Posts
    1,313
    So I pulled the burner out, and cleaned up around the pilot. Not that I saw anything there to begin with.

    As far as the reset button, I wasn't sure just what it was, and I even bypassed it, thinking it may be the problem.

    Still no dice. I am guessing that the valve is bad.

    Frustrating...

    Off to have a cold shower... at least I live in the desert!

    Brandon
    "When you can't make them see the light, make them feel the heat." - Ronald Reagan

  19. #19
    Banned



    Join Date
    Jan 2011
    Location
    Color Me Gone
    Posts
    8,401
    Try taping it in place, I had same problem, pilot light would go on in start-up pilot light position and then it would go off when rotated into final spot. Discovered that it it was backing off, so I fully rotated into place and duct taped it into place.

  20. #20
    Boolit Master mroliver77's Avatar
    Join Date
    Mar 2005
    Location
    Northwest, Ohio
    Posts
    2,922
    Quote Originally Posted by Phoenix View Post
    All my gas appliances are less than 2 years old and they all have pilots, brand new Bosch tankless hot water heater brand new range from Ge
    I have been away from working on them for a few years but everything new we installed had igniter bars and no standing pilot. I thought the feds had outlawed standing pilots on new appliances. Thanks for the information.
    J
    "The .30-06 is never a mistake." Townsend Whelen

    "THESE are the times that try men's souls. The summer soldier and the sunshine patriot will, in this crisis, shrink from the service of their country; but he that stands by it now, deserves the love and thanks of man and woman. Tyranny, like hell, is not easily conquered; yet we have this consolation with us, that the harder the conflict, the more glorious the triumph."
    Thomas Paine

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check