07-25-2022, 04:53 PM
I was at work and got a text from my wife saying the power was out but it should be back on in a few hours. Long story short; when I got home that evening the power was still out and the anticipated time to have the power restored was the next day. We went to Costco and got a generator, this wasn’t the first time we had power outages. The cheapest generator was a Firman T07573 so it came home with us and it worked great. It seems to offer more power than I used so now I’m wondering what all I can run with it.

Is there a way to connect the generator to the house wiring and possibly eliminate some extension cords?

Thanks in advance for your time and effort.

redneck1
07-25-2022, 04:59 PM
If it outputs 220v and you first disconnect the main breaker you can back feed into any 220v outlet ( stove , dryer ) to power the house .

Be sure to turn off high use items like a well pump , hot water heater etc etc

Bobbers
07-25-2022, 05:02 PM
Working in an electrical department in a big box store. I have seen a lot of people hookup power to their house in unsafe and dangerous way. I usual suggest a Generator transfer switch, I have installed them on my last 4 houses. They make several different models depending on wattage.
302529

Hossfly
07-25-2022, 05:04 PM
Most power cos. Offer a safe way to attach a gen to meter weather it be auto or manual that will not back feed into the grid. I would call them and maybe save a life.

elmacgyver0
07-25-2022, 05:11 PM
Yes, there is, you can do it with a transfer switch (the right way) or you could feed it into a dryer, or welder outlet.
If you go the cheap way, be sure you disconnect the fuse that supplies power to your house.
The reason is if you hook to an outlet without disconnecting the mains you have a god chance of killing the poor lineman that is trying to restore power to your home.
Since you are asking this question, I assume your knowledge of electrical wiring is limited.
My recommendation would be to hire a qualified electrician to install a transfer switch for you.
The peace of mind knowing the job was done right is well worth the added expense you will pay to have the job done right.

Pipefitter
07-25-2022, 05:12 PM
First of all, this solution does not meet electrical codes, that being said, here is what I do for my generator/power outage problems. I bought a generator inlet plug, (a male plug in a lockable box) and wired it to a spare 220V breaker in the house electrical panel. When the power is interrupted the first thing you do is switch off the main breaker so that you don't backfeed the power lines, You dont want to be providing power to your neighbors, and providing a dangerous situation to the guys working on "dead" power lines. Also, when the power does come back online the difference in the waveform from the electric company and the output of your generator will burn out the coil on your generator.
once you are positive your main breaker is in the OFF position you can start your generator and switch the spare breaker to the ON position. When you notice that your neighbor's lights are back on, switch the spare breaker to the OFF position and disconnect the generator from the inlet box before turning the main breaker to the ON position.

The way to meet electrical codes is to have a licensed electrician to install a switch panel that allows the generator to run certain circuits in the breaker panel when the power goes out, and will cut the generator from the panel when the power comes back on.

XDROB
07-25-2022, 05:27 PM
I had to get a new breaker box due to kitchen upgrade. At that point I had the electrician put Ina box that had room to put a power transfer breaker in. So I can switch it over to generator power. Then ran a wire to the outside so I could run my generator. I have natural gas for heat and stove. My lights are either led or florescent so a low draw electricly house. I don't have to be selective on what I turn on. But I also don't go around and turn everything on.

I think in most states it's Illegal to back feed into the main lines. You could kill the guy trying to restore power and get yourself into some big legal problems. Be safe pay an expert to hook it up.

Sent from my SM-S908U using Tapatalk

Winger Ed.
07-25-2022, 05:33 PM
It's doable, but kind of expensive to have done properly.

No more than our power goes out and we have to run a generator-
I got the recommended heavy duty extension cords and live with them to run the refrigerators, window unit AC, and a few lights.

dverna
07-25-2022, 05:41 PM
I did for years and it is safe to do if you do it right. But I would not trust my fiancé to do it right.


Now, I have a whole house generator.

ascast
07-25-2022, 05:51 PM
Sometimes the home brew solution is illegal as well as unsafe, non-code, blah, blah. But really you don't want to kill somebody or hurt them. Thast said, oddly my house has a 220 outlet for my welder near the garage door. And I have a lead that fits my generaTOR THAT FIT THAT WELDER PLUG. ( SRY i AIINT REKEYING) Keep in mind your frig/freezer need about an hour a day run time. Maybe an hour every twelve hours. Water pump as needed to flush toilets wash up a bit. It's not so bad running a couple cords and switching as needed. Running an electric dryer or stove or other heating device is not a good idea. I have a small propane cook stove for that, and wood stove. It's all part of life in the boonies.

elmacgyver0
07-25-2022, 05:53 PM
I did for years and it is safe to do if you do it right. But I would not trust my fiancé to do it right.


Now, I have a whole house generator.

Smart man.
I would like a whole house generator but so far, I have resisted.

gc45
07-25-2022, 05:56 PM
If you want to tell me to shut up go ahead, heard it before, but my job is partly keeping people safe..
Being a certified licensed electrician first, then back to school for my professional engineering degree, let me say this:

People should not suggest back feeding from a generator, period. Yes there are some with proper knowledge of doing this but most everyone will not know how to keep themselves out of trouble so please do not suggest to an uninformed homeowner your idea or give encouragement least he or her get injured, or someone kids, god forbid.
Do you want that on your conscience? The world if full of barnyard repair, some works fine, some is darn dangerous and having seen several fires from them, be ware!

Now, to be safe rather than sorry, have your power panel looked at by an expert, it won't cost much if anything to have an electrical company or contractor come out and give you an estimate to change over your panel to allow for safe generator connections; and there are several ways it can be done cost wise to both be safe and allow power to the home.. Just remember those store generators will not run everything and to buy one that will is very costly and expensive to put in..The proper contractor can discuss all this with you, make suggestions and give you costs for every possibility that fits your needs..
good luck and please be safe! your kids will love you for it!

Ickisrulz
07-25-2022, 06:18 PM
We have a 5500 watt generator and a transfer switch. Works great for what we need since our power doesn't go out often. We are able to run the well pump and several circuits.

I installed the transfer switch myself, it wasn't too hard and not too expensive (hardest part was drilling a big hole through brick). It is safe and easy to use.

Forget the suicide cord.

fc60
07-25-2022, 07:22 PM
Greetings,

I learned this the hard way.

When power is restored, disconnect the cables from the generator, close the fuel feed, and let it run the fuel out until the motor dies.

This prevents the carburettor from gumming up.

Also, spend the extra money for NON ALCOHOL GAS and add some preservative.

Last, run the genset once a month for an hour connected to the house circuits.

Have you noticed the genset only fails when the power goes out and it is cold?

Cheers,

Dave

NyFirefighter357
07-25-2022, 08:06 PM
I ran a 30amp generator for years through my dryer outlet, shutting off the main breaker first & major appliances like a/c's, stove & well. Allowing me to selectively use them. I recently purchased a 50 amp generator and decided I would set it up correctly so it would be easier for my wife, kids of neighbor to get power if I wasn't home. I purchased a 50amp inlet box, the breaker interlock, a 50 amp 220V breaker, 6ft of 6/4 wire by the foot at HD & a 25ft cord. When connecting to the whole house you need to remove the bond on the generator between the neutral & ground in doing so though You may loose the use of GFI outlets on a generator. I needed to wire the 50amp breaker to the 1-3 position in my panel so the interlock would work. The interlock prevents the generator inlet breaker from being in the on position when the main breaker(s) are on. The inlet box I got has an LED light that lights up if there is power. The one I chose is a twist lock with a secondary collar lock like an RV inlet, I chose the cord accordingly to match. I had to move some breakers to get the new 50 amp breaker into position. I spent about $250 in materials and wired it in about 2 hours. The interlock mounts to the breaker panel cover between the main breaker & generator breaker. The generator & interlock come with stickers to place on the breaker panel. The only thing I haven't done is relabel my breakers. When I do I will indicate by color what breakers to leave off. I have some breakers that I keep normally off like an extra 220V stove we don't use & dedicated breaker for the electric heater in my garage. At some point I am also going to install a couple of emergency lights, one facing my breaker panel, one to lite up the garage where the panel is and one to lite where the generator is stored.

MrWolf
07-25-2022, 08:50 PM
Be smart and get the transfer switch. As others stated, very easy to kill a lineman or someone. I got tired of the cords and went with a whole house generator. Love it (except when the stink/asian lady bugs shorted out my transfer switch and fried my furnace for almost four weeks this past winter - not fun).

Plate plinker
07-25-2022, 10:55 PM
Just curious what a whole house generator has cost those who have them? Still using a portable unit that really is inadequate.

Winger Ed.
07-25-2022, 11:40 PM
Just curious what a whole house generator has cost those who have them? Still using a portable unit that really is inadequate.

It depends on how big it is, but $3-4,ooo is about where they start, plus the install.
Then the bigger they are, the more expensive they are to feed.

Noah Zark
07-26-2022, 12:34 AM
If it outputs 220v and you first disconnect the main breaker you can back feed into any 220v outlet ( stove , dryer ) to power the house .

Be sure to turn off high use items like a well pump , hot water heater etc etc

Not necessarily. Many 220v generators do not have a neutral, which is needed to provide 110v in house circuitry if "backfeeding a 220v outlet." A house dryer or range circuit has the two 110v legs and a neutral, which provides the 110v for control power to the appliance. With most 220v generator outlets there are the two 110v legs and a ground, which is not the same as a neutral.

For this and other reasons it is best to get a professional electrician involved.

Noah

redneck1
07-26-2022, 04:21 AM
Well don't tell my house that it won't work , it hasn't figured that out yet and I'd hate to over educate it and cause it to start voting democrat

Noah Zark
07-26-2022, 06:13 AM
Well don't tell my house that it won't work , it hasn't figured that out yet and I'd hate to over educate it and cause it to start voting democrat

It works in your house because the neutral and ground are tied together either in the breaker panel or someplace along the way in the house (not preferable at all). Common in older houses, but not all localities permit that, especially those who have rigid and vigorous code enforcement.

Noah

redneck1
07-26-2022, 07:19 AM
Gee , I guess us people out in the nether region's who aren't electricians and follow the code by bonding nuetral with the ground at the service panel are doing things all wrong and need hooked up to them new fangled electrons that flow in New and improved ways .

Now do tell how those electrons I'm backfeeding care if that wire is supposed to be nuetral or ground ?

And yea I know the e and u are transposed , I'm to lazy to fix it .

Noah Zark
07-26-2022, 07:44 AM
Not at all what I am saying. I live in the sticks too.

It works for you because of the bonded neutral and ground. It won't work that well for homeowners whose electrical contractors followed the recent versions of the NEC when installing the service and did not bond neutral to ground. Like a former co-worker, who fried his $1800 refrigerator. All I'm saying is one size doesn't fit all when it comes to feeding 220V from a two-wire-and-ground generator outlet.

Noah

Half Dog
07-26-2022, 08:08 AM
Thanks for sharing your experiences and thoughts. It looks like I’ll be looking for a transfer switch.

bedbugbilly
07-26-2022, 08:28 AM
Sometimes the price of hiring a professional is money well spent to make sure an installation is done correctly and according to Code. As a former firefighter as well as having worked fire.rescue, I have been on more than one "run" for house fires as well as rescues where someone had cobbled up wiring who "thought" the knew what they were doing" - and unfortunately, at least two involved electrocutions. If a job is worth doing, it's worth doing the right way. Your home, your appliances are all "investments" that you have worked hard to get . . . . and you family members are irreplaceable . . . . . so don't take "shortcuts".

Rich/WIS
07-26-2022, 10:15 AM
Added a Generac 13KW during a remodel back in 2003, runs on propane and kicks in atomatically30 seconds after it senses power loss. Came with the appropriate power transfer switch, all wiring for the electrical connections and clear and easy to follow installation instructions. IIRC cost back then wqs about $2500. Runs rhe well (220V),gas and outdoor wood furnaces and a few lights and recptacles in the house and kitchen, but not connected to the other 220V items such as electric stove/ovens or clothes dryer. Will cycle once a week to exercise itself.

farmbif
07-26-2022, 10:23 AM
neutral and ground both end up in the same place in every installation ive ever seen just two separate wires that eventually end up in the ground,.
but I'm no electrician only know from looking that wiring that electricians have done. running a generator adds up real quick with $4 gal gas.

Half Dog
07-26-2022, 02:00 PM
Costs? I have briskets in the freezer.

How often do you turn your generators on and for how long? Right now I’m mostly concerned about the frozen/cold food storage.

Hossfly
07-26-2022, 03:36 PM
Once a week for 12 min. Is what mine is set to test, and you cant defeat that except turn it off. It will show and defects such as battery problems. And give diff color light if needs attn.

.429&H110
07-26-2022, 03:37 PM
It's always cheaper to do it right the first time.

Fairbanks AK routinely loses power, so everybody has a generator.

Nobody mentioned: Don't run it in the garage with the door closed!
Just saying. There is one in every crowd, even in Fairbanks.
Every time the lights go out you can expect a casualty report.

Working propane service, I met a lot of neat propane rigs, professionally installed.
Propane is the "best" standby because it keeps. But how much is in your tank?
City gas is cheap, already to go, but will the utility keep it coming SHTF?
Diesel fuel keeps well with preservative.
Modern gasoline is not a good small engine fuel.
The stuff is like paint thinner with varnish in it.

When the lights go out, and stay out, so do the fuel trucks and gas stations.
Do you have fuel for a day, week, month, or year?

BLAHUT
07-26-2022, 04:25 PM
Be safe put in a transfer switch if you put in hole house go with lp fuel does not go bad>

Winger Ed.
07-26-2022, 05:19 PM
Costs? How often do you turn your generators on and for how long? Right now I’m mostly concerned about the frozen/cold food storage.

The refrigerators are our big concern too.
We have one of the dual fuel ones that's I think a 7500 watt. The plan is to run it a a couple hours every few hours.
It uses about a gallon an hour of fuel. I've accumulated 10 of those swap out at the store size tanks.
Then there's the gasoline option if I run out of those. Along with a few gas cans I rotate out to the truck and lawn mower,
I keep a 12V electric pump to suck gas out of the cars and boat.

I run it a hour or so every year.
If the battery ever konks out, I can jump it off the car, borrow the lawn tractor battery, or even rope start it.

It didn't hit us, but the power company that supplies folks a short distance away had an outage that was for four days.
That's the longest I've seen here. I figure I can make it if that happens to us on just propane.

gc45
07-26-2022, 10:42 PM
So guys, there is a big difference between Neutral and Ground. I will attempt to show those differences here.

Neutral (or the white wire) is referred to in design terms as "The Grounded Conductor". It is this Grounded Conductor that allows the home to have both 230v and 125v. The reason Neutral is important for most all systems is the fact that if Neutral is disconnected or should fail, say at the meter or panel, or any sub-service down stream, your 125v circuits will go to 230v and will cause you lots of trouble..Neutral is always needed for lights, outlets and any other loads that run on 125v..Lose the Neutral and things like radios, tvs, lights and other can be seriously damaged or ruined..Never ever disconnect this Conductor (white) with the power on. If needing to do so, be sure all loads are turned off first and no current flows..

Additionally, Neutral also carries all unbalanced loads meaning; the house or farm has a 230v service, if one hot leg has 50 amperes load, the other hot leg has 40 amperes, the neutral will be carrying 10 amperes load and this folks can kill if touching the uninsulated wire ends. Some think the Neutral is not dangerous but they are wrong! Disconnected Neutrals on energized systems are trouble, so be aware if you take on working with this stuff! It takes just 0.6 amperes to cause heart failure in some folks, let that not be you!

The Ground wire in the Service and in branch circuits is called "The Grounding Conductor"
this wire is generally seen when above the ground as Green is color or bare copper. Some cases the Ground is Black and wrapped with Green tape on the ends. Regardless of colors it is used throughout as a Bond to help in short circuits where equipment fails and can cause things that are current carriers like metal from becoming energized and hurting someone. Example: years back, things like drills and power saws had metal cases and their motors could fail, short out and energize the metal case and injure some one. Now they are cased in plastic that is a non-current carrier and much safer..If having a lathe or other power equipment always be sure the exterior is well grounded. Household appliances are metal so be sure to always connect the Grounding Wire properly or your Wife could have frizzed hair!

Now, at the Main Service, both the Neutral and ground wires are landed on the neutral bar or other screwed on terminal block but the result is the same. There is, or should be a Ground Rod outside with its own ground wire coming into the panel and connected to the Neutral Bar..This allows any faults that travel via the Ground wires to "go to Ground" via the Ground Rod and not back to the power company equipment via the Neutral Wire, etc...

Main Panels with sub-panel feeders going to say, out buildings, barns etc use a 4-wire feeder of 2 Hots, one Neutral and one Ground Conductor. The last two wires are not connected together inside the sub panel but rather the Neutral is "floated" and does not touch the panel metal or Ground wire. This is done by not installing the Sub Panels Neutral Ground Screw and also by adding a separate Ground bar that is mechanically bonded to the panel. this method prevents shorts or faults traveling back on the sub panels Neutral Conductor to the Main Panel. Another story yes but you get the idea...Wire that outbuilding incorrectly and you could have "voltage or faults" running on the Neutral. There is more to this but you get the idea...It is good to consult local authorities as to proper code for your area on outbuildings...hope this helps someone but if only one, it was worth the time to write it!

lightman
07-26-2022, 10:56 PM
Just curious what a whole house generator has cost those who have them? Still using a portable unit that really is inadequate.

When I retired (read that as no longer having a bucket truck in the driveway) 7 years ago I bought a 22 KW Generac. A local farm store had them for right at $5000 including a transfer switch and a concrete pad. That was a very good price at that time and I would expect that unit to be a good bit more now.

MrWolf
07-27-2022, 05:26 PM
Once a week for 12 min. Is what mine is set to test, and you cant defeat that except turn it off. It will show and defects such as battery problems. And give diff color light if needs attn.

Mine runs every Wednesday around 1:00 pm. I bought this back in 2018 from Costco.
HONEYWELL 20KW STANDBY GENERATOR W/ TRANSFER SWITC
Item # *1117344*
$ 3,699.99
Had it wired by an electrician who also ran about 75' to my garage and wired a panel there plus an outside rv panel for around $2,500 if I remember right.

Brokenbear
07-27-2022, 09:31 PM
Yes to the transfer switch ..it is not even an option ..
In my absence even my electronics challenged wife can understand and easily affect the change over
My Champion 9500W electric start inverter gen set is in a portable storage shed sized to hold 2 BIG trash cans ..the flex tube exhaust runs out the side through triple wall stove pipe and turns upward clamped to a "T" post with a flapper cap on top ..this sits 60' from my house
I have a garden hose reel mounted in the "gen shed" with a 75' cord that reaches my outside's locking covered receptical
I have a vertical mounted screened vent intake louvered low on one end and a powered shuttered exaust fan on the other end ..the set up draws air across the equipment very nicely..
I did not wire to run AC (but could)
An INVERTER type gen set IS NOT an option it is a requirement ..that decision was pointed out to me by my HVAC guy who says even my new gas furnace has computer chip in
I run it the first of each month for an hour and also have solar charging wired to the gen set battery
NOTE: Champion gen sets have the patented "cold start" system
I keep 10 5 gallon gas cans treated with Stabil and the gas is alcohol free from CooP ..stored near by in a separate outside bin
Through the summer I slowly burn in our vehicles the 5 gal cans and refill in October winter is our power risk
Important thought for me was I was shocked how fast these 8,9,10,000W go thru propane ..Like a BBQ grill 20# would not get you thru a night ..for a 3/4 day need a serious sized propane tank will be needed and in many areas that means buried ..
I have less than $2000 in the whole shebang
Bear

MrWolf
07-28-2022, 09:02 AM
Forgot to mention I have a 500 Gallon propane tank just for the generator. Think it cost me about $1,000 new and installed. I dug the line for it.

lightman
07-28-2022, 09:27 AM
Important[/B] thought for me was I was shocked how fast these 8,9,10,000W go thru propane ..Like a BBQ grill 20# would not get you thru a night ..for a 3/4 day need a serious sized propane tank will be needed and in many areas that means buried ..
I have less than $2000 in the whole shebang
Bear

I was real thankful to have natural gas available when I installed mine.

725
07-28-2022, 09:31 AM
I had an electrician put in a sub-panel. Can't back up into the regular power lines so a man on the pole is never in danger of a shock. When the power goes out, I can go out and start my generator and then go to the sub-panel to energize the lines for the well pump, freezer, fridge and one or two duplex plugs for minimal lighting. Even if the power is out for a day, a week or more, I have the basics covered. Is it perfect comfort? No. It is "emergency" service. I heat with coal from a hand fired, so heat isn't even in the equation.

Mal Paso
07-28-2022, 09:36 AM
Get A Transfer Switch! Too easy to make a mistake and fry something or Someone. I have a transfer switch built into my main panel.

I switch the whole house but the subpanel transfer switches allow you to be selective about what you power up on generator.

Big Tom
07-28-2022, 10:42 AM
I pre-installed a transfer switch box myself (minus hooking it up to the breaker board), hired an electrician to run the cables to the breakers that I wanted to cover. Paid $250 for the electrician about $150 for the switch box and now have a great solution that covers everything in the house I need to cover (minus AC as my generator is only 3.5 KW).

dverna
07-28-2022, 08:33 PM
Lots of ways to cover your needs.

My first install was a Transfer Switch and I installed it myself. Pulled a permit and had it inspected so I was covered by insurance.

When I moved to my current place, I back fed the panel with an interlock that will not allow the mains to be energized when I am back feeding.

https://www.ebay.com/itm/274635376671?_trkparms=amclksrc%3DITM%26aid%3D1110 006%26algo%3DHOMESPLICE.SIM%26ao%3D1%26asc%3D24067 8%26meid%3D550e7fe1b4c843d399e7de15c420c7c8%26pid% 3D101195%26rk%3D1%26rkt%3D12%26sd%3D274608771572%2 6itm%3D274635376671%26pmt%3D1%26noa%3D0%26pg%3D204 7675%26algv%3DSimplAMLv9PairwiseWebMskuAspectsV202 110NoVariantSeedKnnRecallV1WithNode2Vec&_trksid=p2047675.c101195.m1851&amdata=cksum%3A274635376671550e7fe1b4c843d399e7de1 5c420c7c8%7Cenc%3AAQAHAAABIFVvFeUTQhL4KP79koL%252B 4Ydgokeb2CQrAyC%252BOwbdpQetV2qAC7C3Vu0XLY04JD2l71 qihjhRi6NHnF8%252BhgXS2aYrSe2gbn68aOiuHVBnxF63FWbH 8sgqw1LzoNSvkqaQUqzLM7OrS78u3%252F%252BCrP1y4ihV0e 4dKNQp7YUrxE1vxPIRAYUAYvHlgubpoESnL8Zy0XKebQB02hQ7 TNM11lCT2zV5bynwwybnf3Dga2rTo45SYQtB2CN9HnxN1Fgb8Q MyZj4H%252BpWSJcyJrODL9fCUC3yXwl9J8cwk9shLHNNq1ssT oKPUHcQ8fAZUEGb%252B7Dwi3iRmPy8rEv5C78Xznjul1Q3y2Z LnrmFpgi6Dkhugz9onJxgQpxjVBrIz4IGbzbGtcw%253D%253D %7Campid%3APL_CLK%7Cclp%3A2047675


Three years ago, got a Generac whole house unit.

Geezer in NH
07-29-2022, 08:06 PM
Working in an electrical department in a big box store. I have seen a lot of people hookup power to their house in unsafe and dangerous way. I usual suggest a Generator transfer switch, I have installed them on my last 4 houses. They make several different models depending on wattage.
302529winner!!

I run a 7500 watt portable gas gen. Have a plug in with 6 circuits on it. 1-220V for the well pump 1-120V for oil furnace, 1120v for 2 freezers, 1-120v for fridge, 1 for a lighting circuit to light the interior partially. Cost of Generator $500 cost of transfer switch $190 [self-installed as I held a Master electricians license then]

On the second generator in 30 years.

My son at 14 years old said once when power was down, I hate blizzards as he had been snow-blowing and shoveling roofs all day I'm going to take a hot shower.