PDA

View Full Version : Central AC blower died



Dieselhorses
05-04-2020, 11:39 PM
Trying to see if there are any HVAC pro's here. Couple of hours ago it started getting "stuffy" in house. Got up and checked thermostat and by God it was approaching 80! Had it set to 74. Well I changed the thermostat to one of the older ones we kept, no change. Checked all the breakers-fine. Climbed in attic, removed cover to view cage fan. There is a microswitch on left side of cover so when removed-disconnects circuit. When depressed I just hear a low buzzing noise. I'm hoping this is just the capacitor. All was running perfect 2.5 hours ago! Any advice appreciated.

DukeConnors
05-04-2020, 11:53 PM
It's sort of dangerous but if you spin the fan (use a stick not your hand) while the motor is humming, and the fan starts, it is probably a cap.

Be careful they start pretty fast. Dont lose your trigger finger.

wv109323
05-04-2020, 11:58 PM
Usually there is one capacitor for the fan and compressor. Sometimes the capacitir is swollen or stinking when bad. There is a fuse for control circuit. The buzzing may be a transformer. Good luck.

Dieselhorses
05-05-2020, 12:03 AM
Tried to spin fan and quickly depress microswitch by controller. This is not the outside condenser but by evaporator in attic. Yea, spinning fan don't work. Buzzing noise coming from the controller box left of fan panel. Thanks for input.

NyFirefighter357
05-05-2020, 12:42 AM
Get into the control panel with a tester, I prefer a multi-meter. See if you have power to the fan, If you do you may have blown a speed. If you have power and spinning the fan doesn't work the speed is n/g. Check the wiring diagram & connect another speed to see if it works. If you don't have power trace the power, see if you are getting power out of the control, if yes then check any safety's like the door switch or the float switch on the pan or condensate pump. If your not getting power out of the control panel you may have a bad contact on the board. If this is the case you can usually remove and flip over the board & find where the solder melted off a contact. Re soldering the connection usually fixes this. Also check if you have 24-40V AC on the low voltage side.

metricmonkeywrench
05-05-2020, 08:18 AM
If you do need a motor after the troubleshooting is done look up Genteq motors, highly recommended by my trusted A/C guy.

https://www.regalbeloit.com/brands/Genteq

tinsnips
05-05-2020, 09:43 AM
Pull the blower assembly out try hooking the blower motor up power out side of the furnace controls. If it still don't run go get a new blower motor they are not that expensive. Some motors come with the mount welded to the motor if so you can buy a belly band to make a universal motor fit. Universal motors are a lot cheaper than brand ones are. While you have the blower out wash the wheel also check if you have a secondary coil that might need cleaning. The coil is right ahead of where the blower mounts in the furnace.

truckjohn
05-05-2020, 09:55 AM
Honestly - it's almost always the capacitor. Just replace it - it probably costs like $15.00

My AC repair buddy clued me in on American vs Import capacitors... The imports *barely* last 8 months.. Since it's his business and he doesn't want to give away free callbacks - he only uses American made capacitors - and they usually go well over 2-years. They only cost a bit more - like $20 vs $15.

Dieselhorses
05-05-2020, 11:53 AM
Get into the control panel with a tester, I prefer a multi-meter. See if you have power to the fan, If you do you may have blown a speed. If you have power and spinning the fan doesn't work the speed is n/g. Check the wiring diagram & connect another speed to see if it works. If you don't have power trace the power, see if you are getting power out of the control, if yes then check any safety's like the door switch or the float switch on the pan or condensate pump. If your not getting power out of the control panel you may have a bad contact on the board. If this is the case you can usually remove and flip over the board & find where the solder melted off a contact. Re soldering the connection usually fixes this. Also check if you have 24-40V AC on the low voltage side.



So I called a well recommended AC company here locally and fellow told me 140.00 to change just capacitor and 300.00 total to change motor and capacitor, includes labor. I think the latter would be more cost efficient.

UPDATE: just discovered that overflow pan full of water! Float switch was up/closed so duuhh! Drained water manually now everything works now just have to unclog line! Thanks for everyone's suggestions! (I feel like an idiot).

bangerjim
05-05-2020, 12:08 PM
I was going to suggest the drain pan! I had that happen to our upstairs AC a few years ago. Float systems prevents your upstairs room under the air handler from getting flooded with condensate overflow!!!! You have lots of humidity down there and you should blow the drain line out every spring. Bugs love to make nests in those lines.

If it had been just a motor cap, your motor would have been EXTREMELY HOT and the thermal kickout switch internally in the motor would have been cycling it off and on to prevent a fire.

Get out your air compressor and blow 80# or so back up thru the downstairs outside drain vent. that will clear it! My AC guy recommends pouring a cup of Clorox bleach down the line every spring, but getting the attic is too much work, so I use the compressed air thing.

glad you are not out a few hundred $$!

Dieselhorses
05-05-2020, 02:44 PM
I was going to suggest the drain pan! I had that happen to our upstairs AC a few years ago. Float systems prevents your upstairs room under the air handler from getting flooded with condensate overflow!!!! You have lots of humidity down there and you should blow the drain line out every spring. Bugs love to make nests in those lines.

If it had been just a motor cap, your motor would have been EXTREMELY HOT and the thermal kickout switch internally in the motor would have been cycling it off and on to prevent a fire.

Get out your air compressor and blow 80# or so back up thru the downstairs outside drain vent. that will clear it! My AC guy recommends pouring a cup of Clorox bleach down the line every spring, but getting the attic is too much work, so I use the compressed air thing.

glad you are not out a few hundred $$!

It's a relief yes, but not out the woods yet, have to strategically figure out to clean drain line. Drain exits the coil box then makes a hard right to direction of exterior wall then goes down. A few inches from the unit in attic there's a tee with about 8" of pipe sticking up like a vent. If I blow air in there then it'll just blow back into the coils. Need some sort of "quick disconnect" after that I guess?

skeettx
05-05-2020, 02:59 PM
I just used Clorox and water (50/50) to eat up the algae
Drilled a hole in the drain PVC in the attic
and then used a Coleman funnel with the felt
removed to add the solution,
then covered the hole up with an EAR plug.

https://larrythelanternguy.com/2018/12/09/1970-80s-aluminum-coleman-no-0-filtering-funnel/

https://www.globalindustrial.com/p/safety/ears/hearing-protection/classic-earplugs-310-1060?infoParam.campaignId=T9F&gclid=Cj0KCQjwncT1BRDhARIsAOQF9LkAU49Glu6KwdlLvWg1 1l8oyU-mtItUtJwYJlx09tq7iAQDgZ3iB5waAiBTEALw_wcB

Mike

Dieselhorses
05-05-2020, 05:16 PM
I just used Clorox and water (50/50) to eat up the algae
Drilled a hole in the drain PVC in the attic
and then used a Coleman funnel with the felt
removed to add the solution,
then covered the hole up with an EAR plug.

https://larrythelanternguy.com/2018/12/09/1970-80s-aluminum-coleman-no-0-filtering-funnel/

https://www.globalindustrial.com/p/safety/ears/hearing-protection/classic-earplugs-310-1060?infoParam.campaignId=T9F&gclid=Cj0KCQjwncT1BRDhARIsAOQF9LkAU49Glu6KwdlLvWg1 1l8oyU-mtItUtJwYJlx09tq7iAQDgZ3iB5waAiBTEALw_wcB

Mike

Will give that a try! Looks like right after it makes right turn about 5 ft. away from unit there is another "T" with a pipe fitted inside hole of hallway bathroom vent. I guess it's a backup.

NyFirefighter357
05-05-2020, 06:21 PM
Get into the control panel with a tester, I prefer a multi-meter. See if you have power to the fan, If you do you may have blown a speed. If you have power and spinning the fan doesn't work the speed is n/g. Check the wiring diagram & connect another speed to see if it works. If you don't have power trace the power, see if you are getting power out of the control, if yes then check any safety's like the door switch or the float switch on the pan or condensate pump. If your not getting power out of the control panel you may have a bad contact on the board. If this is the case you can usually remove and flip over the board & find where the solder melted off a contact. Re soldering the connection usually fixes this. Also check if you have 24-40V AC on the low voltage side.


So I called a well recommended AC company here locally and fellow told me 140.00 to change just capacitor and 300.00 total to change motor and capacitor, includes labor. I think the latter would be more cost efficient.

UPDATE: just discovered that overflow pan full of water! Float switch was up/closed so duuhh! Drained water manually now everything works now just have to unclog line! Thanks for everyone's suggestions! (I feel like an idiot).



Ding, Ding. Ding!

Dieselhorses
05-05-2020, 08:34 PM
Ding, Ding. Ding!

HAHA, I'm learning. Doesn't intimidate me just cuz it ain't got a ram, handle and a die on it.

BeeMan
05-05-2020, 10:46 PM
Need to clear a condensate drain line without going in the attic to pressurize it or risk blowing a apart an unglued joints in the drain line? Put a shop vac set up to pick up liquid on the outlet end. Use a wet rag to seal the difference in diameter between the drain line outside diameter and the shop vac suction hose ID. Works like a charm, clears the line, and no risk of blowing apart a weak or unglued drain line. Then add a tee in the line right downstream from the evaporator coil and add a touch of bleach once or twice a year to kill stuff growing in the line. Save yourself a service call, damaged ceilings from an overflowing drain pan, etc..

One more drain line tip: a low spot can collect cold water, condense water on the outside of the drain line, and drip condensate water on the ceiling, making you think there is a leak. Pipe just needa the low spot eliminated to prevent this.

On the original concern with the blower motor not running, the cap is likely. But don't just assume, measure supply voltage and current draw to make sure you don't have a control board problem. Not much stinks as much as replaing a motor and capacitor to find out you overlooked a bad control board and get to replace it as well.

Lessons learned by an HVAC tech....

Jniedbalski
05-05-2020, 11:41 PM
Bleach is the easiest to use and it always works for algae. Here in se Missouri it’s a two to three times a year thing to do. If you don’t want your Ac peeing on the floor. I Do Ac work for over 35 years u would not believe some of the stuff I have seen.

NyFirefighter357
05-05-2020, 11:55 PM
I haven't tested this but copper or zinc strips are added to roof to prevent moss and algae from growing on a roof. Algae is what grows in the condensate trap and clogs the drain. I think I found a use for a couple of those zinc wheel weights, lay a couple of big ones in your drip pan. The oxidation of the zinc kills the algae. You can also try a handful of old copper pennies or a piece of copper or galvanized flashing. Make sure you put it in the path of the water & it's big enough not to fall into the drain. You might tie 4-5 wheel weights together They also sell tablets you can treat you pan with that work like urinal cakes. I'd bet those wheel weights would be enough though.

bangerjim
05-06-2020, 12:44 PM
My clogging problems were not algae but wasp and insect nests about an inch up in the end of the ground end of the drain line. Hard s a rock! Here in the desert, we only get condensate for 3-4 months in the summer when the DP goes above 50F. Plenty of time for insects to build nests. Only air pressure will clear them. Some ac guys use a little device that uses a CO2 cart for pressure. One quick blow and the line is clear, and no messy compressors and extension cords needed.

Dieselhorses
05-06-2020, 08:01 PM
Day 2. Have to once again empty pan. Water appears to be draining through pipe but something tells me the first pan under evap. coils is leaking into bottom pan tripping the float. Have to get to the bottom of this.

skeettx
05-06-2020, 08:25 PM
See if you can push some weed eater mono down the pipe

Dieselhorses
05-06-2020, 11:26 PM
See if you can push some weed eater mono down the pipe

Will try that. Come to find out drain line only goes to bathroom vent pipe in attic and NOT to outside of house. Makes too many turns before draining into big pipe. I’m gonna simplify it.


Sent from my iPhone using Tapatalk

popper
05-06-2020, 11:41 PM
Make sure filter is clean. High humidity and low flow, coils freeze and no cool. Plugged line keeps humidity high. PVC pipe, use vinegar vs bleach. Bleach is OK while moisture in the pipe but will hurt the PVC when weather (AC) is dry. New code has inside drain and outside drain. Inside ones are pain to keep algae out. One of mine gets into the ptrap and stays there.

akajun
05-07-2020, 11:17 AM
Will try that. Come to find out drain line only goes to bathroom vent pipe in attic and NOT to outside of house. Makes too many turns before draining into big pipe. I’m gonna simplify it.


Sent from my iPhone using Tapatalk

was gonna say, you may have a partial blockage in the vent line or the bathroom. Climb up on the roof and check it out, maybe run a small hand powered snake down the vent and the drain.
My units all have a cap that can be removed on the pvc drain line. The one year I forgot to put the chlorine tablets in it it clogged up. A quick blast with a air compressor cleared it out and poured bleach down the drain. Problem is that a few days later all the dead gunk fell and again blocked the drain. Again a quick blast and more bleach and now I remember to drop the tablets in every yrear.

Dieselhorses
05-07-2020, 04:08 PM
Going to follow everyone's advice here for sure! Just checked the attic and the pan is bone dry! Only thing I did last night was remove cover on side and peer inside to view coil condition (somewhat dirty so I took an old fine brush taped to a stick and gently swiped em). When I replaced cover I did have a roll of the shiny tape and sealed all edges. That's all I did differently! Still going to put liquid Drano in drain pipe! I'm wondering, if the coil housing isn't sealed good, wouldn't that cause more condensation? (Not to mention I would be cooling attic too). Also investing in coil cleaner. Pardon me for dragging this out!

skeettx
05-07-2020, 04:14 PM
Drano??

https://www.superiordrain.com/are-liquid-drain-cleaners-harmful-to-pipes

Dieselhorses
05-07-2020, 05:18 PM
Drano??

https://www.superiordrain.com/are-liquid-drain-cleaners-harmful-to-pipes

That's what the AC guy said to use. Not going to use but an ounce or two.

NyFirefighter357
05-07-2020, 05:43 PM
https://skipthewarehouse.com/rectorseal-ezt-113b-economy-trap-kit-with-brush?network=g&device=c&keyword=&campaign=935705900&adgroup=pla-294682000766&gclid=CjwKCAjw4871BRAjEiwAbxXi216cPD55wEeMCT4Sd_m2 wx-8kKD9d1cD2vEMiZVcY3ihSSFevY0avhoC208QAvD_BwE

Dieselhorses
05-07-2020, 08:50 PM
https://skipthewarehouse.com/rectorseal-ezt-113b-economy-trap-kit-with-brush?network=g&device=c&keyword=&campaign=935705900&adgroup=pla-294682000766&gclid=CjwKCAjw4871BRAjEiwAbxXi216cPD55wEeMCT4Sd_m2 wx-8kKD9d1cD2vEMiZVcY3ihSSFevY0avhoC208QAvD_BwE

Doesn't look like anything what I have but for 11.00 I probably could use it! Just went back up in attic and poured about a cup down the hatch, pan still dry. Air kicked on while I was up there and felt a few cold breezes coming from around plenum, fix that right quick with magic silver tape!

Mr_Sheesh
05-11-2020, 02:26 AM
Could you put a fine mesh globe around the end of the drain tube, to block insects, maybe? Or an aquarium air stone?

Alferd Packer
05-11-2020, 03:46 AM
Could you possibly snake in a new drain line and abandon the old one?
Run the new drain line so it can make a more straight thru exit to drain.

Frosty Boolit
05-11-2020, 06:40 PM
I usually find the hum to be the control transformer.