I have an Inkbird ITC100VH PID That I can't seem to get set right. Below is a list of the setting that I have in the memory. I set the sensor Calibration to a pot of boiling water.
Melted lead temperature 750 F taken with a insertion thermometer 524 C with PID. According to the conversion chart that should be 975.2 degrees F.
The thermocouple is a Perfect Prime TL1815 K-Type Sensor Probes Metal Head Probe for K-Type Probe Thermocouple Sensor & Meter in Temperature Range from 0 to 800 °C
You can see my problem.
HiAL Upper Alarm Limit 9999
LoAL Lower Alarm Limit -1999
dHAL Maximum Deviation Alarm 9999
dHAL Minimum Deviation Alarm 9999
dF Hysteresis 0.1
Ctrl Control Output 1
Itergral 540
P Differential 1
t Hysteresis time 120
Ctl Control Period 1
Sn Input Sensor 0
dIP Decimal PointPosition 1
dIL Input Lower Limit 0
dIH Input Upper Limit 1000
SC Sensor Calibration -62.6 (set to boiling water)
oP1 Output mode 0
oPL Output Lower Limit 0
oPH Ouput Upper Limit 100
ALP Alarm Function 0 (No Alarms Hooked Up)
CF System Function 2
Addr Address 1
bAud Baud Rate 9600
dL Input Digital Filter 0
run Run Mode 2
Loc Lock Function 40