    Question PID controller for Lead Furnace Question

    If you were going to build a seperate PID Controller to control the lead pot but wanted to wire a switch to allow direct power to the pot until the lead melted and then flip the switch to control the temperature where in the attached diagram would you wire it in at? Click image for larger version. 

Name:	AutoPotControl Model (3).pdf 
Views:	360 
Size:	93.4 KB 
ID:	37326

  2. #2
    Boolit Bub kitsap's Avatar
    Join Date
    Nov 2010
    Location
    Western Washington State
    Posts
    59
    From another thread.

    PIDSwitch-Model.jpg

  3. #3
    Boolit Master Sonnypie's Avatar
    Join Date
    Jul 2011
    Location
    Saugus, in the State of Socialist Republic of California.
    Posts
    1,226
    Between T1 and L1 of the SSR (Solid State Relay). AKA: On the terminal block T1 & T4. (T1 on the left, T4 on the right.)
    The Neutral is T2 & T3.
    (Pay close attention. If you screw it up, you will blow it up and have some expensive junk)

    When the switch is closed (on), it bypasses the controllers output and puts straight line current to the furnace.
    Once you reach melt, you can open the switch (off) and that puts the SSR and PID in the circuit controlling things.
    Label the switch as BYPASS, or PREHEAT.
    Set your Lee control to 5 or 6 as a safety devise for when you forget it is bypassed.

    Also, install a thermowell for your thermocouple. It'll last longer.
    God Bless America!

    Sittin here watchin the world go round and round...
    Much like a turd in a flushing toilet.

    Shoot for the eyes.
    If they are crawlin away, shoot for the key hole.

    NRA Life Member
    CRPA Life Member

    Magnificent!
    The basic flaw with Science is man.

  4. #4
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    Quote Originally Posted by Sonnypie View Post
    Between T1 and L1 of the SSR (Solid State Relay). AKA: On the terminal block T1 & T4. (T1 on the left, T4 on the right.)
    The Neutral is T2 & T3.
    (Pay close attention. If you screw it up, you will blow it up and have some expensive junk)

    When the switch is closed (on), it bypasses the controllers output and puts straight line current to the furnace.
    Once you reach melt, you can open the switch (off) and that puts the SSR and PID in the circuit controlling things.
    Label the switch as BYPASS, or PREHEAT.
    Set your Lee control to 5 or 6 as a safety devise for when you forget it is bypassed.

    Also, install a thermowell for your thermocouple. It'll last longer.
    No Clue!

    1 Setting the Lee Control to anything but high will defeat the PID Control.

    2 Warm up is like Freeway Miles. Not much wear and tear. I can see the LED and hear the heating element. It is on until it approaches set point then cycles deliberately as it figures how to hold the set temperature. A standard relay would do the job but because of the high number of cycles, once the pot reaches temperature, a solid state relay is often used. This Is The SSRs Job and what it was built to do. You don need no estinkin bypass.

    Sorry but...........
    Mal

    Mal Paso means Bad Pass, just so you know.

  5. #5
    Boolit Man
    Join Date
    Oct 2011
    Location
    Aurora, CO
    Posts
    90
    So I was planing on building my own PID controller with the bypass too. So is there any benefit to installing a bypass?
    Respectfully,

    Powell

  6. #6
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121

    No Bypass

    I looked up the specifications for Auber's $15., 25 amp Solid State Relay and it's designed to handle a one cycle surge of 275 amps so it could handle the Lee max theoretical incandescent load Times 4+.BUT My lee pot is 6 amps Resistive. Just measured it Cold, 20 Ohms, into 120 Volts is 6 Amps Cold and a little less warm. No Big Surge. Don't know how the rumors get started. Auber's SSR FAQ:http://auberins.com/index.php?main_p...d=10&chapter=0

    The SSR will generate about 8 watts Of Heat controlling the lee pot. I have mine bolted to the inside back of the project box with vents above and below.

    This is good technology. Watch out for hot Lead not an extra switch.

    I set my Lee Pots to High which is on all the time, when plugged into the PID, but if your Lee Control is in question take it out of the circuit like snuffy says next post.
    Last edited by Mal Paso; 11-09-2011 at 10:39 AM.
    Mal

    Mal Paso means Bad Pass, just so you know.

  7. #7
    Boolit Master



    snuffy's Avatar
    Join Date
    Feb 2007
    Location
    Oshkosh Wi.
    Posts
    1,747
    Yeah, no need for no steenkin bypass.

    As for the lee heat control, get it completely out of the circuit. Take the top off the lee control tower, take the jumper off the thermostat under the knob, remove it from the heater element, then move the hot wire from the cord that goes to the other side of the thermostat and plug it direct onto the heater element.

    Otherwise the thermostat will open when it gets hot inside the tower, defeating the pid control. The lee thermostat is a simple open or closed bi-metal thermostat, that senses heat inside the tower. Which is why it has giant temp. swings from full to nearly empty.
    He is your friend, your partner, your defender, your dog.
    You are his life, his love, his leader. He will be yours, faithful and true, to the last beat of his heart.
    You owe it to him to be worthy of such devotion."

    “At the worst, if he fails, at least fails while daring greatly, so that his place shall never be with those cold and timid souls who know neither victory nor defeat”--Theodore Roosevelt

  8. #8
    Boolit Master

    MikeS's Avatar
    Join Date
    Feb 2011
    Location
    Weston, Florida
    Posts
    2,152
    I was concerned about setting up a bypass, but was told by a friend that's a lot more familiar with electronics than I am (after he looked at the schematic of my PID controller) that with a SSR you really don't need to worry, and can just startup cold with the PID in the circuit, and that's what I do. While the lead is heating up the PID just supplies constant current, and doesn't start switching on/off till it's close to the set temp. So far so good, my PID controller hasn't lost it's blue smoke yet.
    - MikeS

    Want to checkout my feedback? It's here:
    http://www.castboolits.gunloads.com/...d.php?t=136410

  9. #9
    Boolit Man
    Join Date
    Oct 2011
    Location
    Aurora, CO
    Posts
    90
    Quote Originally Posted by snuffy View Post
    Yeah, no need for no steenkin bypass.

    As for the lee heat control, get it completely out of the circuit. Take the top off the lee control tower, take the jumper off the thermostat under the knob, remove it from the heater element, then move the hot wire from the cord that goes to the other side of the thermostat and plug it direct onto the heater element.

    Otherwise the thermostat will open when it gets hot inside the tower, defeating the pid control. The lee thermostat is a simple open or closed bi-metal thermostat, that senses heat inside the tower. Which is why it has giant temp. swings from full to nearly empty.
    Whoa, Whoa, Whoa Snuffy,

    You are blowing my mind with all them big words and things...

    I am electrically challenged and since I don't have my pot here to look at and reference, can you explain, in more detail, how to remove the Lee heat control from the circuit. I'm sure it's very easy, but I'm having a hard time picturing what you are saying. Thanks!
    Respectfully,

    Powell

  10. #10
    Boolit Master



    snuffy's Avatar
    Join Date
    Feb 2007
    Location
    Oshkosh Wi.
    Posts
    1,747
    Powell, the term "jumper" is what I call the short wire that goes from the thermostat to the heater coil. It has a bayonet type sliding connector on it's end. Simply remove that short wire, take the wire off other side of the thermostat, connect it directly to the heater element. Done!

    Now you can plug the original cord into a receptacle on the pid cabinet, or hard wire it into the circuit. I put a receptacle in my pid cabinet, because I use it on 2 pots, will be using it on three as soon as I install a thermocouple/temp probe in an old saeco melter.



    You also have to be able to plug in the thermocouple to use on more that one pot. Be sure to use the same wires that connect the TC through the plug, to the PID and use that yellow plug available from Auber. And maintain polarity.

    He is your friend, your partner, your defender, your dog.
    You are his life, his love, his leader. He will be yours, faithful and true, to the last beat of his heart.
    You owe it to him to be worthy of such devotion."

    “At the worst, if he fails, at least fails while daring greatly, so that his place shall never be with those cold and timid souls who know neither victory nor defeat”--Theodore Roosevelt

  11. #11
    Boolit Man
    Join Date
    Oct 2011
    Location
    Aurora, CO
    Posts
    90
    Snuffy,

    Ok, great! Breaking it down Barney style (or Army style if you please) works great for me! thanks
    Respectfully,

    Powell

  12. #12
    Boolit Master Sonnypie's Avatar
    Join Date
    Jul 2011
    Location
    Saugus, in the State of Socialist Republic of California.
    Posts
    1,226
    Quote Originally Posted by Mal Paso View Post
    No Clue!

    1 Setting the Lee Control to anything but high will defeat the PID Control.

    2 Warm up is like Freeway Miles. Not much wear and tear. I can see the LED and hear the heating element. It is on until it approaches set point then cycles deliberately as it figures how to hold the set temperature. A standard relay would do the job but because of the high number of cycles, once the pot reaches temperature, a solid state relay is often used. This Is The SSRs Job and what it was built to do. You don need no estinkin bypass.

    Sorry but...........
    "If you were going to build a seperate PID Controller to control the lead pot but wanted to wire a switch to allow direct power to the pot until the lead melted and then flip the switch to control the temperature where in the attached diagram would you wire it in at?"

    That was the OP's question.
    I gave him a direct and correct answer. A way to bypass the SSR.
    And having the Lee control in there as a safety device. And a way to make his thermocouple last indefinitely by using a thermocouple well.
    But hey, you geniuses just roll along with your $200 controls for a $63 lead pot.
    You are right about one thing though.
    You are a sorry butt.

    God Bless America!

    Sittin here watchin the world go round and round...
    Much like a turd in a flushing toilet.

    Shoot for the eyes.
    If they are crawlin away, shoot for the key hole.

    NRA Life Member
    CRPA Life Member

    Magnificent!
    The basic flaw with Science is man.

  13. #13
    Boolit Buddy
    Lee W's Avatar
    Join Date
    Mar 2005
    Location
    Upstate NY
    Posts
    290
    Quote Originally Posted by Sonnypie View Post
    But hey, you geniuses just roll along with your $200 controls for a $63 lead pot.
    You are right about one thing though.
    You are a sorry butt.

    Sonny,
    I check all of these PID threads and it seems you cannot grasp the idea of someone wanting a precisely controlled lead pot. What is so difficult to understand? A constant temperature will yield consistent boolits if the process is done consistently.
    Pretty easy.

    I might be the only one to say it, but leave you negative comments about the cost to yourself. It is not your money and your comments are not helpful to the discussion at all.

    Thanks.

    Lee W

  14. #14
    Boolit Master



    snuffy's Avatar
    Join Date
    Feb 2007
    Location
    Oshkosh Wi.
    Posts
    1,747
    But hey, you geniuses just roll along with your $200 controls for a $63 lead pot.
    You are right about one thing though.
    You are a sorry butt.
    My lee 4-20 would swing 75 degrees from full to ¼ full. 75 degrees HOTTER! Maybe you like frosty boolits or weight swings of 5 grains in a 250 grain boolit, buT I don't. I like them all to be the same size and weight, and a constant temp does that.

    Speaking of butTs, what is going on with yours in your avatar?
    He is your friend, your partner, your defender, your dog.
    You are his life, his love, his leader. He will be yours, faithful and true, to the last beat of his heart.
    You owe it to him to be worthy of such devotion."

    “At the worst, if he fails, at least fails while daring greatly, so that his place shall never be with those cold and timid souls who know neither victory nor defeat”--Theodore Roosevelt

  15. #15
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    Quote Originally Posted by Sonnypie View Post
    "If you were going to build a seperate PID Controller to control the lead pot but wanted to wire a switch to allow direct power to the pot until the lead melted and then flip the switch to control the temperature where in the attached diagram would you wire it in at?"

    That was the OP's question.
    I gave him a direct and correct answer. A way to bypass the SSR.
    And having the Lee control in there as a safety device. And a way to make his thermocouple last indefinitely by using a thermocouple well.
    But hey, you geniuses just roll along with your $200 controls for a $63 lead pot.
    You are right about one thing though.
    You are a sorry butt.

    Ok

    Everything past T1 and L1 in post 3 was utter nonsense from someone who has never done it.

    Why try to scare people. This equipment is so well protected and would be difficult to hurt it even if you did cross a wire. I have yet to see a post from someone with a bad experience.

    The PID Control won't work with the Lee Control set to 5 or 6.

    A thermowell will screw up your readings. The probe is $7 and stainless steel and if it can handle me ripping it out and soldering it back in it will last as long as I care about.

    I spent $128 because I wanted the Deluxe Box, Extra Probe, and Plugs. I've seen the controllers for sale here for $15 and a lot of guys here have put PIDs together for $50. For better temp control than a $250 pot, it's worth it.
    Mal

    Mal Paso means Bad Pass, just so you know.

  16. #16
    Boolit Master Sonnypie's Avatar
    Join Date
    Jul 2011
    Location
    Saugus, in the State of Socialist Republic of California.
    Posts
    1,226
    Mal,
    42 years as a professional in electrical controls and Industrial and Utillity electrical maintenance. Those are my quantification.
    So it can only be utter nonsense to someone who really has not a grasp on electrical control.
    If you knew anything about electrical control, you would see that what I posted is really two explanations to do the exact same thing, bypass the electronic control section and apply direct line voltage and current to the output.
    Precisely what the OP asked for. A way to bypass.

    Scare people? Advising they pay attention is scaring people?
    Do you know anything about electricity? Did you look at his pdf file? Can you read a schematic?
    Tell us, oh wise one, what happens if somebody not in this post decides to attempt to hook up their own bypass switch, and instead of the terminals and circuits described, they hook T1 and L2 (The neutral) together?
    Bam!
    And the control is instant junk. A dead short on the SSR's output.

    A thermowell will screw up your readings?
    More than having crud build up insulating the probe from the heat?
    Yeah, sure. That is why every major piece of critical equipment has the thermocouple just hanging in the process fluids bobbing around and being beat on.
    Yeah, you're right. Industrial control is wrong. All those industries controlling processes and critical utility equipment really don't know what they are doing.

    My Lee pot will easily run over temperature at 5-6 settings. That's why I have a thermometer in it to monitor my alloy.
    IF one wants to put a solid state control on the pot, it is prudent to have the original control in the circuit as a safety device. Safety devices help reduce human errors, and equipment failures.
    Let's try something really basic, what is an over temperature device for in your home's heater? Or the oven?
    So you advocate that since there is a temperature control there anyway, the high limit device is unnecessary?
    That is exactly what you are advocating. I have seen not one of these temperature controls that have an over temperature, or high limit, designed into them.
    Merely settings and control. All based on the thermocouple input. No secondary safety devices, no high limit or over temperaturecontrol.
    Normally (in my experience) they will fail in the open condition. But I have seen them fail closed and run away. I've been on failure analysis teams for major catastrophic equipment failures.

    Even a portable electric heater has an over temperature limit switch, and a tip over switch.
    Just the facts. But hey, what do I know?

    But you boys have fun. When it burns out, just buy another one.
    God Bless America!

    Sittin here watchin the world go round and round...
    Much like a turd in a flushing toilet.

    Shoot for the eyes.
    If they are crawlin away, shoot for the key hole.

    NRA Life Member
    CRPA Life Member

    Magnificent!
    The basic flaw with Science is man.

  17. #17
    Boolit Master
    Join Date
    May 2011
    Posts
    761
    'bout time for a moderator high colonic

  18. #18
    Boolit Mold
    Join Date
    Apr 2011
    Posts
    14
    Geez guys. Sorry I brought up the subject. I just wanted to know if it was possible. I'm just getting into casting and was asking questions on this since I had read that you probably shouldn't heat up a cold pot with the PID hooked up and that it should be wired direct for a cold pot and then switch it over to controlled once the lead is hot. Guess from reading the above that it can be used on a cold pot with no bad things happening. Thanks for everyone's input

  19. #19
    Boolit Master

    theperfessor's Avatar
    Join Date
    Dec 2007
    Location
    Evansville Indiana
    Posts
    2,746
    I built a dual PID controller with Auber parts. I use it to control a hot plate and a Lyman Mag 20. I didn't put in a power switch at all. I make sure both are turned down/off, then I plug them into the PID box, plug the PID box power cord in to the wall, and turn on the units all the way on. Seems to work fine. The SSRs don't even get warm.

    Note: I'm NOT an electrical engineer, and I know nothing about Lee pots or their internals. I'm nit giving expert advice. I'm just sayin' what works for me.

  20. #20
    Boolit Master

    Join Date
    May 2011
    Location
    200 miles south of the center of the United States
    Posts
    645
    I just built a PID controller and love it ! After reading this and the other thread about switching out the SSR/PID during warmup, I thought about it a while and came up with a low cost solution...I just plug the pot in directly to an outlet till stuff starts to melt, then plug it into the PID controller.

    Works for me.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check