  1. #61
    Boolit Master Jim22's Avatar
    Join Date
    Oct 2020
    Location
    Eastern Washington
    Posts
    592
    The reason for this advice is that the appliance is designed for the lower amperage. The circuit in the wall will support the higher amperage but the wiring in the appliance may not. Be safe. Get the proper circuit breaker to be safe.

    Jim

  2. #62
    Boolit Master
    Join Date
    May 2010
    Location
    Green Valley
    Posts
    763
    Posted this before so I will post it again
    I was in a wire fire 100 amp 480v just would not open
    The main finally opened and stopped the fire
    Circuit breakers can weld their contacts and just don't help
    Change out old breakers when you can.

    Doing service work I found an old lady running on one thirty amp sloblo fuse so I composed

    "Old Miss Johnson had a fuse e i e i o
    on this fuse she had a tv e i e i o
    with a toaster here and a light bulb there
    here a hair dryer, there a heating pad
    she only worked them one at a time e i e i o

    So I installed a 200A panel, and chased out the knob and tube.
    She still does not know why.
    I am sorry that it cost a lot of money to install that microwave.

  3. #63
    Boolit Master
    Join Date
    Mar 2013
    Location
    Northeast
    Posts
    2,925
    Per the owner's manual:
    "This appliance must be supplied with the proper voltage and frequency, and connected to an individual, properly grounded, 40 amp (minimum) branch circuit protected by a circuit breaker or time-delay fuse."

    So, what would be the "proper circuit breaker"?

  4. #64
    Moderator


    Winger Ed.'s Avatar
    Join Date
    May 2007
    Location
    Just outside Gun Barrel City, Texas
    Posts
    9,708
    Quote Originally Posted by Battis View Post
    So, what would be the "proper circuit breaker"?
    40 or bigger.
    The appliance will draw what it wants/needs.
    You need a circuit breaker and properly size wires to accommodate it.
    The breaker protects the wires from getting a overload for their size, heating up, and possibly starting a fire.

    Bigger is OK. Running it on a 50 or 60 amp wires & breaker works like plugging in,
    or running a single 100 watt light bulb on a 20 amp circuit & breaker.

    Those people who have a breaker that trips easily, and just swap in a larger rated one 'because it fits'
    in the panel can burn down their house.
    In school: We learn lessons, and are given tests.
    In life: We are given tests, and learn lessons.


    OK People. Enough of this idle chit-chat.
    This ain't your Grandma's sewing circle.
    EVERYONE!
    Back to your oars. The Captain wants to waterski.

  5. #65
    Boolit Master
    Join Date
    Jul 2008
    Posts
    4,388
    Quote Originally Posted by Battis View Post
    Per the owner's manual:
    "This appliance must be supplied with the proper voltage and frequency, and connected to an individual, properly grounded, 40 amp (minimum) branch circuit protected by a circuit breaker or time-delay fuse."

    So, what would be the "proper circuit breaker"?
    As an old electrical teacher would say "The 40 amp breaker will afford you better protection."

  6. #66
    Boolit Master

    Join Date
    Feb 2016
    Location
    Fl.
    Posts
    1,609
    Quote Originally Posted by BD View Post
    geo, I'd agree with you with the obvious exception of Federal Pacific breakers and panels. They are definitely out-dated, and dangerous. Many jurisdictions require them to be replaced in any commercial dwelling before you can pass the Fire Marshall's inspection.
    As a side comment regarding breakers:
    We bought a beachfront condo in the late 90’s that had been built by the Kaiser Development Corp in the late 60’s. The same Kaiser that built WW2 Liberty Ships and Industrial Facilities all over North America. Fourteen years later we decided to sell it. The purchaser had the place inspected. The condo unit breaker panel was a 100 amp Federal Pacific that, according to the inspector was dangerous, banned, and had to be replaced prior to closing.
    That condo development was one building, four floors, twenty units on each floor. Coincidentally all the electrical mains, meters and feeds for the twenty units on our floor were in an electrical vault/room next door our unit. Virtually EVERY breaker and disconnect, and all the feeds and sub-feeds were also Federal Pacific. This was (and still is) true for the entire development.
    I pointed this out to the purchaser and put him in touch with the insurance company that carried our Association policies. He bought our condo, FP breakers and all.

    That building was 100% cast Concrete and CMU construction with steel studs throughout. The only wood it contained were the kitchen / bathroom cabinets and personal furnishings. When we sold our condo (2014) the development still conformed to the latest Miami-Dade Construction Codes, including those for wind, hurricane and fire safety.

    If I understand it correctly the Federal Pacific fire problems were the result of overheating and this was (I think) attributed to aluminum wiring. Whatever the cause, FP breakers and replacement parts were still available at HD in 2014.
    A fire requires a fuel source.

  7. #67
    Boolit Master Hannibal's Avatar
    Join Date
    Sep 2013
    Location
    East of KCMO
    Posts
    2,212
    Quote Originally Posted by Bmi48219 View Post
    As a side comment regarding breakers:
    We bought a beachfront condo in the late 90’s that had been built by the Kaiser Development Corp in the late 60’s. The same Kaiser that built WW2 Liberty Ships and Industrial Facilities all over North America. Fourteen years later we decided to sell it. The purchaser had the place inspected. The condo unit breaker panel was a 100 amp Federal Pacific that, according to the inspector was dangerous, banned, and had to be replaced prior to closing.
    That condo development was one building, four floors, twenty units on each floor. Coincidentally all the electrical mains, meters and feeds for the twenty units on our floor were in an electrical vault/room next door our unit. Virtually EVERY breaker and disconnect, and all the feeds and sub-feeds were also Federal Pacific. This was (and still is) true for the entire development.
    I pointed this out to the purchaser and put him in touch with the insurance company that carried our Association policies. He bought our condo, FP breakers and all.

    That building was 100% cast Concrete and CMU construction with steel studs throughout. The only wood it contained were the kitchen / bathroom cabinets and personal furnishings. When we sold our condo (2014) the development still conformed to the latest Miami-Dade Construction Codes, including those for wind, hurricane and fire safety.

    If I understand it correctly the Federal Pacific fire problems were the result of overheating and this was (I think) attributed to aluminum wiring. Whatever the cause, FP breakers and replacement parts were still available at HD in 2014.
    A fire requires a fuel source.
    I would be FAR more concerned about aluminum wiring inside a structure than anything else materials-wise. General Electric tried aluminum wiring in locomotive applications. Those that didn't burn up had to have the aluminum wiring removed to be replaced with copper.

    That was a few decades ago. It was never tried again in a locomotive.

  8. #68
    Boolit Grand Master popper's Avatar
    Join Date
    Jun 2011
    Posts
    10,586
    I did the estimate for the ceiling lighting in KCI airport. We didn't get the contract. Company that did was kicked off and we got to replace the Aluminum wiring, cost plus 10%. 350 and 500W mercury lamps in each corner of the cast ceiling. Al wiring cracks when bent sharp and expands - causing insulation failure. One solution in residential is to pigtail the Al with Cu at any switch or receptacle. Kapton insulated Al is a NO-NO. The elec code was written by insurance company and exists for a reason. Oh, beware of big box store breakers!
    Whatever!

  9. #69
    Boolit Buddy
    Join Date
    Nov 2015
    Location
    New Mexico
    Posts
    482
    All this back and forth...Poor OP still can't cook his breakfast, lol!

    I think the obvious best answer is to connect the stove to four 10A circuits wired in parallel...

  10. #70
    Boolit Master
    Join Date
    Mar 2013
    Location
    Northeast
    Posts
    2,925
    All is good. The stove was delivered and set up, had it all checked out professionally (wiring, breaker) and everything is great. The only thing that annoyed me was that to use the air fryer, we had to set it up with WiFi. Set it up, then bypassed it and it works manually without WiFi.
    It was easier buying a car than a stove.
    Thanks for the replies.

  11. #71
    Boolit Master
    BD's Avatar
    Join Date
    Mar 2005
    Location
    Moosehead Lake
    Posts
    1,818
    It is the basic design of the Feral Pacific breakers that is dangerous. They still account for something like 3,000 home fires per year in the US. While I certainly wouldn't be as nervous in a concrete and steel building, an electrical fire would still ruin your day, (week, and month).

  12. #72
    Boolit Master Hannibal's Avatar
    Join Date
    Sep 2013
    Location
    East of KCMO
    Posts
    2,212
    Quote Originally Posted by BD View Post
    It is the basic design of the Feral Pacific breakers that is dangerous. They still account for something like 3,000 home fires per year in the US. While I certainly wouldn't be as nervous in a concrete and steel building, an electrical fire would still ruin your day, (week, and month).
    Can you provide a reference for that figure? I know FP breakers are often viewed as dangerous and perhaps rightly so but I like to know my opinions are based on verified facts.

    Please don't take this as a personal attack, that's not my intent at all. I'd really like to see an information source is my motivation.

  13. #73
    Boolit Master



    MUSTANG's Avatar
    Join Date
    Jan 2012
    Location
    Kalispell, Montana
    Posts
    2,768
    Quote Originally Posted by Battis View Post
    All is good. The stove was delivered and set up, had it all checked out professionally (wiring, breaker) and everything is great. The only thing that annoyed me was that to use the air fryer, we had to set it up with WiFi. Set it up, then bypassed it and it works manually without WiFi.
    It was easier buying a car than a stove.
    Thanks for the replies.
    When our Electric Range destroyed itself due to Main Line Power Surge - We replaced it with a Canadian Built Propane stove because we could not get an Electric, Natural Gas, or Propane Stove that was "USofA" that was not California Compliant. California Compliant inevitably puts all sorts of California Mandated features and controls into it that are not user friendly or controllable; or downright dangerous in an environment that can get to minus 35 Fahrenheit in the Winter and the power goes out.
    Mustang

    "In the beginning... the patriot is a scarce man, and brave and hated and scorned. When his cause succeeds, the timid join him, for then it costs nothing to be a patriot." - Mark Twain.

Page 4 of 4 FirstFirst 1234

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check