    Help with PID

    I just built a PID controller using a PID donated to me (Red Lion T48). I believe it is wired correctly, but when I plug a lamp or Lee lead furnace into it, I'm not getting light or heat. I then plugged in a volt meter and am seeing 95.2 volts going to the output.

    2 questions:
    1) would 95.2 V be too low to power on the lamp or furnace? (meaning the PID is working correctly, but just doesn't have the output power set correctly?)
    2) if the above is too low, what needs to be configured to up the output V? I see % Output Power, which looks likely, but the docs say "Appears only if unit is in Manual Control". The manual then describes "Manual Control" as "and Manual Control (openloop; where the control does not work from the setpoint or process feedback.)"

  2. #2
    Boolit Master

    Mike W1's Avatar
    Join Date
    Nov 2008
    Location
    Rural Sumner, IA
    Posts
    1,317
    Quote Originally Posted by prickett View Post
    I just built a PID controller using a PID donated to me (Red Lion T48). I believe it is wired correctly, but when I plug a lamp or Lee lead furnace into it, I'm not getting light or heat. I then plugged in a volt meter and am seeing 95.2 volts going to the output.

    2 questions:
    1) would 95.2 V be too low to power on the lamp or furnace? (meaning the PID is working correctly, but just doesn't have the output power set correctly?)
    2) if the above is too low, what needs to be configured to up the output V? I see % Output Power, which looks likely, but the docs say "Appears only if unit is in Manual Control". The manual then describes "Manual Control" as "and Manual Control (openloop; where the control does not work from the setpoint or process feedback.)"
    I'd be happy to help if I can but it'd really help to know what the PID model is and the wiring diagram that you used. Maybe best if you PM that info to me along with your email address as that stuff is more easily handled (IMO) via email. Easier to send files or attachments if needed. Quick guess would be a wire hooked in wrong place somewhere.
    Mike

    Benefactor Member NRA
    Life Member Iowa Firearms Coalition
    US Army Vet

    There are two ways to conquer and enslave a nation.
    One is by the sword. The other is by debt.”
    John Adams 1826

  3. #3
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704
    Can you take a picture of your setup?

    I found the manual -> https://www.instrumart.com/assets/Re...P48-Manual.pdf

    You should have a SSR that you are using.
    For discussion we are gonna label the ssr as the picture below shows
    Click image for larger version. 

Name:	s-l1600.jpg 
Views:	38 
Size:	35.4 KB 
ID:	265847

    1 should be incoming power (line)
    2 should be power going out (load)
    3 Positive from your PID controller
    4 neg from your PID controller

    Using your volt meter do the following
    AC VOLTAGE

    wall outlet - check neutral to hot Should be 110-125vac
    SSR - check neutral to #1 Should be the above voltage
    SSR check neutral to #2 (when PID is powered up and is not at set point) should be within 1 volt of the above voltage
    SSR check #1 to #2 should be a very low number if not zero

    DC VOLTAGE

    Check # 3 and # 4 - should be between 3 and 32 vdc most likely 5 to 10 vdc

    Do those checks and provide some pictures if you want me to help you
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  4. #4
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    Here is what I did. I wired it up just to see if it'd work before spending time putting it in a neat enclosure. Given my history with projects, I didn't want to waste time and money only to find it doesn't work (as, well, it turned out not to).

    The green wire going off the picture to the left is the AC power.
    The green wire going off the picture to the right feeds the Lee furnace.
    The Red and white wires at the 12 o'clock of the PID are the thermocouple inputs (8 and 9 on the PID diagram)
    The Red and white wires at the 3 0'clock of the PID are the AC inputs (11 and 12 on the PID diagram)
    The Red and white wires at the 6 o'clock of the PID are the outputs to the SSR (4 and 5 on the PID diagram)

    Click image for larger version. 

Name:	IMG_20200806_225232.jpg 
Views:	42 
Size:	61.6 KB 
ID:	265865
    Click image for larger version. 

Name:	IMG_20200806_225723.jpg 
Views:	49 
Size:	79.8 KB 
ID:	265866

  5. #5
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704
    looks like its wired up right.
    need to verify voltages.

    I ran into a issue a couple months ago which caused me to make a 90 min service call to visit a Master Caster Panel customer.
    The pot would never get up to temp. I checked my voltages and we had 119 vac at the outlet, 119 vac on the line side but only 85 vac on the load side. The SSR was calling for full voltage as its is a ON/OFF device it isn't like a valve were it controls the amount of voltage.
    I replaced the SSR with a spare that I had brought and life was good again.

    The PID pulses the SSR to regulate the temp.
    Typically on initial startup you will see some quick on/off on the SSR (if yours has a light) then it will go solid.
    Once it gets close to the set point it will start flashing again and when at set point it will flash as it is trying to maintain the temp.
    Imagine the SSR as a rocket engine with just a on/off switch. It is either wide open or its off.
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  6. #6
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704
    I think I got something
    Looking over closely at the SSR, I noticed something.

    That model SSR uses 90-280 VAC on the control side.

    I believe that model PID provided a @7 volt output for the SSR.
    That would explain why you aren't getting any heating as you aren't activating the SSR.
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  7. #7
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    Quote Originally Posted by HATCH View Post
    looks like its wired up right.
    need to verify voltages.

    I ran into a issue a couple months ago which caused me to make a 90 min service call to visit a Master Caster Panel customer.
    The pot would never get up to temp. I checked my voltages and we had 119 vac at the outlet, 119 vac on the line side but only 85 vac on the load side. The SSR was calling for full voltage as its is a ON/OFF device it isn't like a valve were it controls the amount of voltage.
    I replaced the SSR with a spare that I had brought and life was good again.
    Sounds similar to what I'm seeing. 119 vac going into the PID, but only 85 vac coming out.

    Quote Originally Posted by HATCH View Post
    Typically on initial startup you will see some quick on/off on the SSR (if yours has a light) then it will go solid.
    Once it gets close to the set point it will start flashing again and when at set point it will flash as it is trying to maintain the temp.
    Imagine the SSR as a rocket engine with just a on/off switch. It is either wide open or its off.
    Mine has a light but it never illuminates.

    Further observations:
    When I put a volt meter on the main control output, I get a 0 vac reading. When I place the volt meter on the output cord (that feeds the Lee furnace), I see 85 VAC. Does that seem like the SSR is broken (stuck in the on position)?

    Quote Originally Posted by HATCH View Post
    That model SSR uses 90-280 VAC on the control side.

    I believe that model PID provided a @7 volt output for the SSR.
    That would explain why you aren't getting any heating as you aren't activating the SSR.
    This, combined with the no light coming on would suggest this is the problem. I don't understand, however, how I'm getting 85 vac going to the furnace if the SSR isn't in the on state.

  8. #8
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704

    Help with PID

    Your getting bleed thru voltage but no current

    Get the correct ssr


    Sent from my iPhone using Tapatalk
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  9. #9
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    Quote Originally Posted by HATCH View Post
    Your getting bleed thru voltage but no current

    Get the correct ssr


    Sent from my iPhone using Tapatalk
    Will do. Does this look like a good candidate?

    Click image for larger version. 

Name:	2020-08-07 19_22_06-Amazon.com_ Inkbird SSR Solid State Relay SSR 40DA for PID Thermostat Temper.png 
Views:	20 
Size:	346.1 KB 
ID:	265910

    https://www.amazon.com/INKBIRD-Solid..._t2_B017W7N4J2

  10. #10
    Boolit Master
    Join Date
    Jul 2008
    Posts
    4,337
    Is #4&5 main control output actually DC voltage. Your SSR is actually controlled by 90-280 volts AC. The OP needs one like the pic in Hatch's post #3.

    That inkbird should work!
    Last edited by jsizemore; 08-07-2020 at 07:44 PM.

  11. #11
    Boolit Master
    Join Date
    Jul 2008
    Posts
    4,337
    Quote Originally Posted by prickett View Post
    Sounds similar to what I'm seeing. 119 vac going into the PID, but only 85 vac coming out.



    Mine has a light but it never illuminates.

    Further observations:
    When I put a volt meter on the main control output, I get a 0 vac reading. When I place the volt meter on the output cord (that feeds the Lee furnace), I see 85 VAC. Does that seem like the SSR is broken (stuck in the on position)?



    This, combined with the no light coming on would suggest this is the problem. I don't understand, however, how I'm getting 85 vac going to the furnace if the SSR isn't in the on state.
    Since your getting 0 vac at the main control output, try changing your meter to DC voltage.

  12. #12
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704
    That inkbird will work.
    Please keep in mind that there is a very slight possibility that the PID May of been damaged by using the incorrect SSR but I am pretty sure it’s gonna be ok.


    Sent from my iPhone using Tapatalk
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  13. #13
    Boolit Buddy dpoe001's Avatar
    Join Date
    Nov 2013
    Location
    PA
    Posts
    116
    i can send you or email you the manual for everything you have or pics on how to wire it up or if it needs it repair board for the pid.

  14. #14
    Boolit Buddy dpoe001's Avatar
    Join Date
    Nov 2013
    Location
    PA
    Posts
    116
    Private message sent on the pid

  15. #15
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    Quote Originally Posted by jsizemore View Post
    Since your getting 0 vac at the main control output, try changing your meter to DC voltage.
    Thanks for noticing my error. I tried DC and am still getting 0 volts. Seems like the PID might be defective? I'm going to try a new SSR first, then a new PID if it still doesn't work.

  16. #16
    Boolit Buddy dpoe001's Avatar
    Join Date
    Nov 2013
    Location
    PA
    Posts
    116
    that str is not DC voltage it is 120 VAC

  17. #17
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    Quote Originally Posted by dpoe001 View Post
    that str is not DC voltage it is 120 VAC
    The input to the SSR I used says 90-260 VAC.

    The output on the PID has a positive and negative terminal. And, the Inkbird SSR I ordered shows input of 3-32 VDC. Based on the PID having +/- terminals I believe the feed to the SSR is VDC.

  18. #18
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,704
    I unsubscribed to this thread so if you need any additional help send me a PM


    Sent from my iPhone using Tapatalk
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

  19. #19
    Boolit Master prickett's Avatar
    Join Date
    Nov 2009
    Location
    Middle Tennessee
    Posts
    805
    I received my new SSR and it does not change things. I believe that the PID isn't sending out a signal to the SSR (volt meter shows 0 VDC coming out). So a new PID is next up

  20. #20
    Boolit Master

    Mike W1's Avatar
    Join Date
    Nov 2008
    Location
    Rural Sumner, IA
    Posts
    1,317
    A quick way to check the PID is to take the TC leads loose on the back of the PID. Short across those 2 terminals with a jumper wire and the readout on the PID should show ambient temperature.
    Mike

    Benefactor Member NRA
    Life Member Iowa Firearms Coalition
    US Army Vet

    There are two ways to conquer and enslave a nation.
    One is by the sword. The other is by debt.”
    John Adams 1826

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check