    Quote Originally Posted by sharps4590 View Post
    Ok, first off 10 amp breakers either are, or, have been available but they are special order and it would be HIGHLY unusual for any electrician to install them unless specifically required for a particular piece of equipment and usually something like that is taken care of at the equipment by a fused disconnect where the fuses are the protection for the equipment and the breaker is the protection for the wiring. As has been pointed out 15 and 20 amp are the most common, 120 volt breaker sizes IN RESIDENTIAL application. The "interrupting current" of residential breakers is 10,000 AIC, "Amps Interrupting Current". I have seen that abbreviated on some residential breakers as "10K AIC" and have a had a lot of customers over the years tell me they have "10 amp breakers" in their panels when they don't. There should be a number 15 or 20 on the either the breaker body or the breaker handle specifying what the amperage is of the breaker. After, as I said, 42 years of doing this for a living I really doubt you have 10 amp breakers. If you do, yours is the first I have ever heard of and I have never seen it.

    I have known of some old time electricians who would put 15 amp breakers on #12 wire and there's nothing wrong with that except that the safe capacity of the wire is not available. As per NEC, in residential applications, #14 wire is good for 15 amps, #12 is good for 20 amps and #10 good for 30 amps, #8 for 40 and #6 for 50 or 60, depending. If those are exceeded one is in violation. After that Section 310-16 is the "go to" article in the NEC for wire ampacities as the type of insulation has a bearing on the capacity of the wire as well as wire size.

    In nearly all commercial applications I've worked on the AIC is specified to be 20K, AIC. I don't remember what it is as voltages got higher as in 277/480 and the old 230/460.
    I went back to the breaker panel and checked again and you are correct. They are marked 10,ooo aic in white letters where the 10 is easy to read and the rest not so much. The actual amperage is a molded number on the handle where it is not highlighted or readily visible, at least to my old eyes. The breakers are actually 20 amp breakers.
    Thank you for the information. You saved me some unnecessary expense and worry.
    Click image for larger version. 

Name:	IMG_0189.jpg 
Views:	28 
Size:	22.7 KB 
ID:	229133
    Last edited by tazman; 10-20-2018 at 06:27 PM.

  2. #22
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,687
    Quote Originally Posted by sharps4590 View Post
    Ok, first off 10 amp breakers either are, or, have been available but they are special order and it would be HIGHLY unusual for any electrician to install them unless specifically required for a particular piece of equipment and usually something like that is taken care of at the equipment by a fused disconnect where the fuses are the protection for the equipment and the breaker is the protection for the wiring. As has been pointed out 15 and 20 amp are the most common, 120 volt breaker sizes IN RESIDENTIAL application. The "interrupting current" of residential breakers is 10,000 AIC, "Amps Interrupting Current". I have seen that abbreviated on some residential breakers as "10K AIC" and have a had a lot of customers over the years tell me they have "10 amp breakers" in their panels when they don't. There should be a number 15 or 20 on the either the breaker body or the breaker handle specifying what the amperage is of the breaker. After, as I said, 42 years of doing this for a living I really doubt you have 10 amp breakers. If you do, yours is the first I have ever heard of and I have never seen it.

    I have known of some old time electricians who would put 15 amp breakers on #12 wire and there's nothing wrong with that except that the safe capacity of the wire is not available. As per NEC, in residential applications, #14 wire is good for 15 amps, #12 is good for 20 amps and #10 good for 30 amps, #8 for 40 and #6 for 50 or 60, depending. If those are exceeded one is in violation. After that Section 310-16 is the "go to" article in the NEC for wire ampacities as the type of insulation has a bearing on the capacity of the wire as well as wire size.

    In nearly all commercial applications I've worked on the AIC is specified to be 20K, AIC. I don't remember what it is as voltages got higher as in 277/480 and the old 230/460.
    Sharps4590 made a good guess. I was thinking the same thing and his later post confirmed it. I've had customers do the same thing. Most residential equipment was once rated at 10K but is being increased to 22K. I'm guessing that this may be because building practices have changed. You once had large lots and long overhead services and now smaller lots with larger underground services are more common. A 10kva transformer and 100 ft of #4 won't produce 10,000 amps of fault current but a 50kva transformer and 100ft of 4/0 will easily exceed that. This is to keep the equipment from failing, or exploding, if it has to operate. Prolly more than most wanted to know about fault current!

    Some breakers or more dependable than others. When I was working I favored Square D's QO line. The older grey handle CH were good too. FPE was notorious for not tripping and in my mind the jury is still out on the older GE's. As to sizes, I have seen 10 and even smaller size breakers but 15 and 20 amp and larger will be about all you will find for sale.

    When I wired houses I never used any wire smaller than #12. Not even for the switch leg. I fused the multi outlet circuits at 20 amps and the single outlet circuits, ie the washing machine, dish washer, ect, at 15 amps. This was just me, many others have done differently.

  3. #23
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,687
    Quote Originally Posted by tazman View Post
    I went back to the breaker panel and checked again and you are correct. They are marked 10,ooo aic in white letters where the 10 is easy to read and the rest not so much. The actual amperage is a molded number on the handle where it is not highlighted or readily visible, at least to my old eyes. The breakers are actually 20 amp breakers.
    Thank you for the information. You saved me some unnecessary expense and worry.
    Attachment 229123
    Your attachment is not working for me but I'm guessing that it may be a picture. You are correct, the breaker rating should be on the handle. It may or may not be in a different color. I'm glad that you did not pay an electrician to change out all of your breakers. Most electricians would have shown that to you before charging you for doing the work, but................

  4. #24
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    14ga is useful when the lighting designer wants 12 switches in a 2x4 wall, otherwise 12ga.

    Square D QO has a 10 amp breaker but I've never seen one in an AC panel. I use them for solar as they are rated to 48 volts DC too.
    Mal

    Mal Paso means Bad Pass, just so you know.

  5. #25
    Boolit Master
    Join Date
    May 2012
    Location
    Outside Rolla, Missouri
    Posts
    2,170
    As LED has become more common I don't see a thing wrong with #14 for lighting. If properly loaded I didn't see anything wrong with it pre-LED. If a conductor is loaded correctly at the 80% of capacity, what's the difference between breaking 4/0 USE-2 at 200 amps or #14 at 15 amps? Both are properly protected.

    I semi-retired about 3 years ago and only work about 15-20 hours a week....and less than that for about 3 more months. I was unaware the residential AIC was being increased. For what you described, lightman, it makes perfect sense. I'll have to watch next time I buy any breakers and see what's on them. Most of what I do these days is change switches and repair fixtures for Grandma....and others....lol! Do a lot of LED updating for my commercial customers. I couldn't agree more with your opinion on breakers. I have found the Homeline, Square D series to be good but when we built I put in QO. I wouldn't get up out of my chair for a GE unless I needed a cheap welder. The tan handled, CH series, by Cutler Hammer, (I assume that's what you're calling gray handled?) I think is as good as QO. I'm kinda still on the fence about their BR series. You sure see a lot of BR switch gear locally and given the cost of Square D I'm not surprised. FPE got in trouble with UL...and for good reason. The old FPE, wide bodied breakers were pretty good but after about '78 or '80 they went to the dogs and those Slim Lines were never worth spit. FPE did make good switch gear. Some of that old stuff I've taken out was built like a tank. I don't believe I've seen more than 1 or 2, 10 amp breakers during my entire career and those were in a BIG hospital....what the heck they were for I don't know, probably a motor load or maybe a little bitty isolation transformer.

    taz, you didn't do anything a thousand others haven't done. Why wouldn't a fella think that's what his breaker was if that's what he saw and didn't know what it meant.

    Ha...just got a service call. Ordinarily I WOULD NOT go on a Saturday afternoon but they're long time customers and it's gonna be down in the 20's tonight. Better go.
    "In general, the art of government is to take as much money as possible from one class of citizens and give it to another class of citizens" Voltaire'

    The common virtue of capitalism is the sharing of equal opportunity. The common vice of socialism is the equal sharing of misery

    NRA Benefactor 2008

  6. #26
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    Quote Originally Posted by sharps4590 View Post
    Ha...just got a service call. Ordinarily I WOULD NOT go on a Saturday afternoon but they're long time customers and it's gonna be down in the 20's tonight. Better go.
    Writing about Service Work disturbs The Force. LOL
    Mal

    Mal Paso means Bad Pass, just so you know.

  7. #27
    Boolit Master
    Join Date
    Sep 2016
    Posts
    2,659
    This a pertinent thread for me.

    I cast on my deck. One outlet there, to which I connected EVERYTHING: casting pot, mold preheating hot plate and lighting for the cooler nighttime sessions. No problems until I also rigged a feeder pot to the casting pot. If all three elements cycle on, the breaker trips.

    I guess the safest thing is to run at least one element on a different circuit, maybe only one each on three circuits?

  8. #28
    Moderator Emeritus


    JonB_in_Glencoe's Avatar
    Join Date
    Mar 2010
    Location
    Land of 10,000 Lakes
    Posts
    15,832
    It depends on the Hotplate, Most old ones are 1500W and it should be run on it's own circuit.
    Two Lee pots (6 amps each) will be fine having both on one circuit.
    That's my 2˘
    ~~~~~~~~~~~~~~
    “If someone has a gun and is trying to kill you, it would be reasonable to shoot back with your own gun.”
    ― The Dalai Lama, Seattle Times, May 2001

  9. #29
    Boolit Master
    Join Date
    Sep 2016
    Posts
    2,659
    Thanks for the suggestion!

  10. #30
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,687
    You might consider running a circuit to your deck just for this purpose. Depending on how your house is wired its entirely possible that the existing outlet could be on a circuit with one of the rooms in your house, thus having other stuff on it. You can calculate the load of your casting equipment by looking at the name plates. The load should be listed as either amps or watts.

  11. #31
    Boolit Master
    Join Date
    Sep 2016
    Posts
    2,659
    You weren't off the mark there, lightman.

    A close gander at the legend on the panel shows that the outside outlet is on a circuit that supplies the whole front of my house: living room, dining room, office, bathroom and deck, about twenty outlets all told, and it's only a fifteen amp breaker. No wonder it tripped.

  12. #32
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,687
    Quote Originally Posted by kevin c View Post
    You weren't off the mark there, lightman.

    A close gander at the legend on the panel shows that the outside outlet is on a circuit that supplies the whole front of my house: living room, dining room, office, bathroom and deck, about twenty outlets all told, and it's only a fifteen amp breaker. No wonder it tripped.
    Its pretty common in residential work to have outlets on a common wall share a circuit. But, thats a lot of stuff on a circuit even though the normal loads in those rooms are pretty light. You can verify what is actually on that circuit pretty easily by turning the breaker off and checking the outlets with a lamp or test light. You might consider getting an estimate on running a dedicated circuit if you plan to continue casting there.

  13. #33
    Boolit Master redhawk0's Avatar
    Join Date
    Apr 2016
    Location
    North East, USA
    Posts
    1,419
    Here is another thing to keep in mind...you're not going very far with that extension cord so NEVER coil up the extra length while its plugged in. If you do it will act as an inductor and heat up enough to melt the insulation of the coiled part of the extension cord. Leave it lay out straight...or just a few loops loosely coiled or random loop diameters if you have to.

    I found this out the hard way before I became an EE. I was an early teen and had a 100 ft cord that I was running a electric fry pan off of our patio. The extra extension cord was wrapped around a "spool" and in less than 5 minutes....pooof.

    redhawk
    Last edited by redhawk0; 10-26-2018 at 11:14 AM. Reason: lousy grammer

    The only stupid question...is the unasked one.
    Not all who wander....are lost.
    "Common Sense" is like a flower. It doesn't grow in everyone's garden.

    If more government is the answer, then it was a really stupid question. - Ronald Reagan

  14. #34
    Boolit Master
    Join Date
    Dec 2017
    Location
    Farmerville,Louisiana
    Posts
    1,357
    Each circuit breaker should only supply 7 outlets including light switch. When I wired my house in 2001. Ended up using 98 outlets,10 in garage one every 6 feet, just for future use, all 12 gauge wire
    Not bragging just listened to older eletriction, except he wanted to soldier all connections, and not use wire nuts.

  15. #35
    Boolit Master
    Join Date
    Sep 2016
    Posts
    2,659
    Thanks for the suggestions, and apologies to namerifrats for the hijack.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check