    My step son is tring to set up his travel tralor. 30 amp plug,80 ft from the breaker box. He ran a 10 gauge wire it wouldnt run the ac. he ran a 6 gauge still no luck.hooked up a genarator everything worked fine. He isn't tripping any breakers? Any ideas I don't have a volt meter
    when the dust settles and the smoke clears all that matters is I hear the words " well done my good and faithfully servant "

    <(*)(()><

  2. #2
    Banned
    Join Date
    Apr 2010
    Location
    SE Iowa
    Posts
    679
    Funny question, Load, length of run determines wire size and breakers as service

  3. #3
    Boolit Master



    Join Date
    Aug 2013
    Location
    South West Texas
    Posts
    734
    #6 copper should do it, aluminum you need to go to #4

  4. #4
    Boolit Master
    Join Date
    Feb 2015
    Location
    Cass county, Michigan
    Posts
    658
    A quick lesson in electricity and RV air conditioners: I was an electrician in 2 different RV plants and an industrial electrician for a few years after that. A 13,500 BTU RV AC will draw about 18 amps when running, figure about 2-3 times that when the compressor starts.

    As a rule of thumb for every 100 feet of wire between the power supply and the motor you need to up-size the wire by one gauge.
    I suspect that you do not have 110 volts at the breaker box due to the wire length from the transformer to the breaker box.
    You can try running a 4 gauge copper wire but that would get expensive.
    I suspect that instead of tripping the breaker you are getting an interrupt from the starter on the AC compressor motor.

  5. #5
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    #10 should do 30 amps at less than 5% voltage drop which is the usual limit.

    #6 should be under 2% voltage drop which is the usual off grid limit. I would suspect the 30 amp plug and whatever is behind it.
    Mal

    Mal Paso means Bad Pass, just so you know.

  6. #6
    Boolit Master

    Plate plinker's Avatar
    Join Date
    May 2012
    Location
    Indiana
    Posts
    2,305
    Quote Originally Posted by Pipefitter View Post
    A quick lesson in electricity and RV air conditioners: I was an electrician in 2 different RV plants and an industrial electrician for a few years after that. A 13,500 BTU RV AC will draw about 18 amps when running, figure about 2-3 times that when the compressor starts.

    As a rule of thumb for every 100 feet of wire between the power supply and the motor you need to up-size the wire by one gauge.
    I suspect that you do not have 110 volts at the breaker box due to the wire length from the transformer to the breaker box.
    You can try running a 4 gauge copper wire but that would get expensive.
    I suspect that instead of tripping the breaker you are getting an interrupt from the starter on the AC compressor motor.

    What he said. The start up is the killer. Also as suggested the power at the outlet may be inadequate. Just for giggles if every other power draw is turned off will it work?

    I would check and see what size wire is behind that 30 amp outlet. Almost bet it is undersized.

  7. #7
    Boolit Master
    rl69's Avatar
    Join Date
    Aug 2010
    Location
    Brookeland Texas
    Posts
    2,848
    Thank you for your responses they helped. They have confirmed what I was thinking.

    He is pulling power from a breaker box inside a home. (30 amp ) the six should have been more then plenty. The ten should have done it? He has given up and says he is going to drop a new service. His wife says he isn't.

    I told him to buy a 50 amp breaker,run that from the house to a breaker box outside the trailer, then Ron his plug from there. We will see where he goes from here.

    is it posable for a breaker to not put out a full load but not trip?
    when the dust settles and the smoke clears all that matters is I hear the words " well done my good and faithfully servant "

    <(*)(()><

  8. #8
    Boolit Master
    rl69's Avatar
    Join Date
    Aug 2010
    Location
    Brookeland Texas
    Posts
    2,848
    We did not see if the ac would work by itself
    when the dust settles and the smoke clears all that matters is I hear the words " well done my good and faithfully servant "

    <(*)(()><

  9. #9
    Boolit Master

    Plate plinker's Avatar
    Join Date
    May 2012
    Location
    Indiana
    Posts
    2,305
    Quote Originally Posted by rl69 View Post

    is it posable for a breaker to not put out a full load but not trip?

    YES. That’s how some fires start.

  10. #10
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,696
    My calculations, based on pulling a full 30 amps at 100ft show that #6 will have a 2% voltage drop. 2% is acceptable. I think you may have another problem. Without a voltmeter you are just guessing.

  11. #11
    Boolit Buddy





    Join Date
    Jan 2010
    Location
    south UP of MI
    Posts
    187
    Dirty connections. Measure the voltage at house, then in trailer, no load should be same value. Apply a stable load like a good sized heater and see how much the voltage collapses at the trailer. The voltage will be dropped on the dirty connection(s), which will be apparent if you can measure it at each connection.

  12. #12
    Boolit Master

    10-x's Avatar
    Join Date
    Dec 2007
    Location
    south eastern coast
    Posts
    909
    Ran a 100 amp service to backyard garage and half, installed 100 amp box with breakers for 240 for irrigation pump, 120 for the GFI recepticles and 30 amp for RV. RV will function with limits with 30 amps but if living in it needs 50amps. Owners manual clearly states one can not operate all elect. componernts on 30 amps. AC and maybe a 120 recpt. or 2 but no high draw components, microwave, water heater or elect. heater. Excellent advice already posted, check panel that feeds 30 amp plug, breaker size? ground ok? lastly borrow meter or get friend with one to check everything.
    10-x

    NRA Endowment
    H.R.M.S.
    N.F.A.C.
    RVN Veteran
    VFW
    "The short memories of the American voters is what keeps our politicians in office"------Will Rogers

  13. #13
    Boolit Master
    Join Date
    Mar 2016
    Location
    SW Wyoming
    Posts
    543
    Spend a few dollars on a volt meter. For about 7 bucks you can get one at harbor freight, or about double that if there is no HF close by. For this price range you will get one good enough for any home need.

    When you say "he ran a 10 gauge wire" do you mean he only ran 1 wire? He should have 3 separate wires, 1 hot (usually black) 1 neutral (white) and 1 ground (green).

  14. #14
    Boolit Grand Master

    Join Date
    Apr 2008
    Location
    Phoenix, Arizona
    Posts
    6,213
    My RV will get the 10 gauge wires hot if I use 2 rv extension cords with the cord from the rv. This would be about the same length as what he is running. I have 2 low draw Coleman a/c units on my rv with a load controller so only one will start at a time. One unit is fine with 2 cords but I try not to do this anymore. Thinking of converting it to 50 amp service.
    My 2005 travel trailer had a Chinese a/c unit on it and it would not start with 2 extension cords, barely with one extension cord. Draw was almost 40 amps when starting.
    I have also noticed that most of the imported wire is not up to the size stamped on the cord.

    Walmart has a decent multimeter for $20.

  15. #15
    Boolit Buddy
    Join Date
    Aug 2005
    Posts
    165
    With all due respect, there is no way an rv a/c unit can draw 40 amps at start up. If it does it would trip the breaker. A rv a/c unit is similar to a in the window unit for a house that plugs into your wall. The start up amps on these is less than 10 amps and run amps should be about 4 or 5 amps. In my humble opinion the op has a compressor problem. Take a look at the capacitor for rust or corrosion at the connections and maybe see if they make a hard start kit for it.

  16. #16
    Boolit Master

    Plate plinker's Avatar
    Join Date
    May 2012
    Location
    Indiana
    Posts
    2,305
    OP states that it worked with the generator. His power source is the likely culprit.

  17. #17
    Boolit Master
    rl69's Avatar
    Join Date
    Aug 2010
    Location
    Brookeland Texas
    Posts
    2,848
    Thanks guys, I found it. What is the first rule in trouble shooting? Start at the beginning,no matter how simple.

    I didn't get there tell late yesterday evening,and started tweaking what he was doing. Today I started at the beginning, where his plug wire went into the trailer, and in big letters it said 120 volts.

    A little embarrassing but no damage done. He needed 6 gauge wire anyway with 120 volts at that distance. Again thanks for the help.
    when the dust settles and the smoke clears all that matters is I hear the words " well done my good and faithfully servant "

    <(*)(()><

  18. #18
    Boolit Master
    Join Date
    Feb 2015
    Location
    Cass county, Michigan
    Posts
    658
    Quote Originally Posted by Steelshooter View Post
    With all due respect, there is no way an rv a/c unit can draw 40 amps at start up. If it does it would trip the breaker. A rv a/c unit is similar to a in the window unit for a house that plugs into your wall. The start up amps on these is less than 10 amps and run amps should be about 4 or 5 amps. In my humble opinion the op has a compressor problem. Take a look at the capacitor for rust or corrosion at the connections and maybe see if they make a hard start kit for it.
    Starting current is ALWAYS greater than running current. The breakers used in residential (and RV) power panels are "time delay" breakers
    If it were an instantaneous trip breaker you would have to set it at 800% of full load amps. Look it up in the National Electrical Code.

  19. #19
    Boolit Buddy
    Join Date
    Aug 2005
    Posts
    165
    As soon as you show me a 13,500 rv a/c that uses 18 running amps.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check