  1. #21
    Boolit Master

    Plate plinker's Avatar
    Join Date
    May 2012
    Location
    Indiana
    Posts
    2,308
    Nice analogy razorfish.

  2. #22
    Boolit Master
    Join Date
    May 2016
    Location
    Hudson Valley NY
    Posts
    1,478
    The real advantage of 220V on large loads is circuit wiring. 20amps needs 12ga wire. If you needed 40 amps for 110v circuit you would need 4ga wire and an equally sized neutral, which is more expensive and harder to through the walls. By using 2-12ga for 220v wires you can divide the amperage between the 2 smaller wires and of course don't need a neutral. And as the lengths get longer the wire needs to be larger.

  3. #23
    Boolit Master
    Mal Paso's Avatar
    Join Date
    Jun 2010
    Location
    Carmel, Ca
    Posts
    4,121
    Quote Originally Posted by NyFirefighter357 View Post
    The real advantage of 220V on large loads is circuit wiring. 20amps needs 12ga wire. If you needed 40 amps for 110v circuit you would need 4ga wire and an equally sized neutral, which is more expensive and harder to through the walls. By using 2-12ga for 220v wires you can divide the amperage between the 2 smaller wires and of course don't need a neutral. And as the lengths get longer the wire needs to be larger.
    8 gauge wire. 40 amps requires 8 gauge wire.
    Mal

    Mal Paso means Bad Pass, just so you know.

  4. #24
    Boolit Grand Master

    dragon813gt's Avatar
    Join Date
    Feb 2012
    Location
    Somewhere in SE PA
    Posts
    9,989
    Quote Originally Posted by Mal Paso View Post
    8 gauge wire. 40 amps requires 8 gauge wire.
    Yep, #4 will handle 70-95A depending on the wire type used.

  5. #25
    Boolit Man
    Join Date
    Feb 2018
    Posts
    90
    I think most of you have overlooked the MOST important reason to get 220V equipment of any kind - Lead pots, air compressors saws etc..... It makes it harder for other people to borrow it from you!!!

  6. #26
    Boolit Grand Master

    dragon813gt's Avatar
    Join Date
    Feb 2012
    Location
    Somewhere in SE PA
    Posts
    9,989
    Quote Originally Posted by mvozz View Post
    I think most of you have overlooked the MOST important reason to get 220V equipment of any kind - Lead pots, air compressors saws etc..... It makes it harder for other people to borrow it from you!!!
    Three phases fixes that problem permanently

  7. #27
    Boolit Master

    alamogunr's Avatar
    Join Date
    Mar 2005
    Location
    Tennessee
    Posts
    4,509
    I guess I'm a little out of my depth here. I always thought that 3 phase was an advantage in large electric motors, primarily in an industrial environment. Does it even work for resistive loads?
    John
    W.TN

  8. #28
    Boolit Grand Master

    dragon813gt's Avatar
    Join Date
    Feb 2012
    Location
    Somewhere in SE PA
    Posts
    9,989

    110 or 220V's

    Yes, it works in resistive loads. Amp draw is lower just like in motors.

  9. #29
    Boolit Master


    Join Date
    Apr 2005
    Location
    Eastern South Dakota
    Posts
    3,662
    alamogunr,

    Yes, that's right. Electric heat is a resistive load so it starts gently and ramps up to full load. A motor is an inductive load and starts with violence (often six time the running current) and then tapers off to running load. In industrial environments there are engineering considerations that can make sense for using a three phase circuit for a heating load but power consumption isn't one of them.

    As an example, the largest heat load I've ever seen is in a glass furnace. The furnace itself was square so they installed a four-phase 180/276 volt set up. One phase in each corner, arcing over to the other corner through the molten glass kept the glass liquid. Drew well over 10,000 amps. Since the furnace was square they needed four phases to arc over to each other. Made an X I suppose though of course you couldn't see it. If it had been triangular three would have been the way to go.

    The poster with the pushing the car up the hill is actually a good analogy, but it only works for inductive loads as described above. Doesn't work for a heat (resistive) loads. Electricity is tricky stuff!


    Cat
    Cogito, ergo armatum sum.

    (I think, therefore I'm armed.)

  10. #30
    Boolit Master

    alamogunr's Avatar
    Join Date
    Mar 2005
    Location
    Tennessee
    Posts
    4,509
    That is interesting. I retired from a factory that made conductors for amperage well over 10,000 amps but I never saw the actual application. I wouldn't be surprised if some of those products were used in that glass furnace.
    John
    W.TN

  11. #31
    Boolit Grand Master

    gwpercle's Avatar
    Join Date
    Sep 2011
    Location
    Baton Rouge, Louisiana
    Posts
    9,298
    Quote Originally Posted by dragon813gt View Post
    No it doesn't. Watts are watts. 10 amps at 110 volts is 1100 watts. 5 amps at 220 volts is 1100 watts. There are lots of reasons for using 220 over 110. Reduced power consumption is not one of them.
    You got that right ! Reduced power consumption is a misconception.
    Certified Cajun
    Proud Member of The Basket of Deplorables
    " Let's Go Brandon !"

  12. #32
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Quote Originally Posted by iomskp View Post
    My definition of using single phase against multiple phase, is that it is easier for two or three people to push a car up a hill than one large man to do the same thing.
    240 is still a single phase in nearly all residential applications.
    Last edited by Boogedy_Man; 03-16-2018 at 03:47 PM.

  13. #33
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Quote Originally Posted by NyFirefighter357 View Post
    The real advantage of 220V on large loads is circuit wiring. 20amps needs 12ga wire. If you needed 40 amps for 110v circuit you would need 4ga wire and an equally sized neutral, which is more expensive and harder to through the walls. By using 2-12ga for 220v wires you can divide the amperage between the 2 smaller wires and of course don't need a neutral. And as the lengths get longer the wire needs to be larger.
    Some applications may still require a neutral....like ranges, dryers, etc...because there's still an unbalanced load.

    The most conservative rating for allowable capacities in copper conductors (60 degrees C) puts 8awg at 40 amps, and 4awg at 70. Of course, there are situations where this would need to be derated, and other situations (such as welders) where smaller conductors could be used due to low duty cycle.

  14. #34
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Quote Originally Posted by Catshooter View Post
    alamogunr,

    The furnace itself was square so they installed a four-phase 180/276 volt set up. One phase in each corner, arcing over to the other corner through the molten glass kept the glass liquid. Drew well over 10,000 amps. Since the furnace was square they needed four phases to arc over to each other. Made an X I suppose though of course you couldn't see it. If it had been triangular three would have been the way to go.
    That's a polyphase setup I'd like to see...how was this power generated?

  15. #35
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Quote Originally Posted by wapiti22 View Post
    Looking to buy a melting pot. Lot's of model come in either 110V or 220V. I have 220V readily available in my garage. What the benefit of one over the other?
    OP...there could be a huge advantage depending on which code your home was built under, and how the electricians decided to design it.

    In this area it is very common for homes to have a single 15A circuit for all garage receptacles and all required outdoor GFCIs...which in my opinion is an absolute disaster.

    The 2014 code changed that practice, but many jurisdictions are still on much older code. I'm not up to speed on the 2017 code, but I believe there may have been even more conservative rules resulting from the popularity of electric cars.

    The shorter answer is what you've already heard....if you have a 120V circuit that you can use without overburdening...there is no advantage.

  16. #36
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Quote Originally Posted by Mal Paso View Post
    This discussion is all single phase 120/240 volt. A 20 amp 120v circuit max is 2400 watts, the recommended safe load is 80% or 1920 watts. 1440 watts for 15 amps. My old pot was 700 watts and the hot plate 1500 so I ran an extension cord from another circuit...
    The 80% rule is for a single piece of cord and plug connected equipment that is not fastened in place. You can safely use 100% of a multiple outlet branch circuit, unless any portion of the load is a continuous load.

  17. #37
    Boolit Master


    Join Date
    Apr 2005
    Location
    Eastern South Dakota
    Posts
    3,662
    Boogedy Man,

    The power was transformed. Three phase 26k incoming. The engineer called it two-phase! It was a very cool place to work in. Worked there three or four times over the years.

    We were working underneath one of the furnaces one time that was running. Lots of steel support system and such. Man came in with us and put a Port a Band down on the ground. It had just had it's cord replaced. When he set it down the ground prong touched a steel support. The cord was still in a wrapped curl from the factory. Didn't take but about a couple of minutes and the cord was smoking. We slapped an Amprobe on it and the ground was drawing nearly 40 amps! Just a few loose killywiggles about.

    The power to the furnace was run around three sides of the furnace in bussing. Two parallel runs of one inch by twelve inch aluminum plate, un-insulated. The busing was about eight feet up so you kinda wanted to watch were you were swinging a stick of conduit!


    Cat
    Cogito, ergo armatum sum.

    (I think, therefore I'm armed.)

  18. #38
    Boolit Master
    Join Date
    May 2012
    Location
    Outside Rolla, Missouri
    Posts
    2,170
    Cast, I've been an electrician for 42 years, passed my Masters Exam in '81. I would be tickled to death to see that furnace you're talking about. Certainly nothing like that around here unless something similar might be at MS&T in one of their labs. They do have some cool toys!
    "In general, the art of government is to take as much money as possible from one class of citizens and give it to another class of citizens" Voltaire'

    The common virtue of capitalism is the sharing of equal opportunity. The common vice of socialism is the equal sharing of misery

    NRA Benefactor 2008

  19. #39
    Boolit Man
    Join Date
    Jan 2018
    Posts
    94
    Catshooter, that's pretty dang cool.

  20. #40
    Boolit Master


    Join Date
    Apr 2005
    Location
    Eastern South Dakota
    Posts
    3,662
    I'm a retired union wireman, worked in Seattle. Some pretty cool installations there.

    I worked at Boeing's wind tunnel site quite a bit. Four point three acres, they had over 80,000 horsepower in electric motors. One was 55,000.

    Their air compressor building has a 6,000 horse primary compressor. When they put it in in '64 is was a 5,000, but that was too small so they pulled it and had it re-wound to six. 4160 volt, across-the-line start! When that starter closed it sounded like a .30-06. In a quarter of a cycle it went from zero to over 3,000 amps. The operator told me that if the incoming voltage was less than 4.2, he'd call Seattle City Light and ask them to raise it. The motor would almost start at that voltage. If it failed he couldn't try again for eight hours so it could cool.

    We replaced the 4 MVA transformer that fed that motor with a new 12.5 MVA unit. It weighed 1/3 of the old one.

    Saw and worked on some cool stuff there.


    Cat
    Cogito, ergo armatum sum.

    (I think, therefore I'm armed.)

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check