Thread: How I wired a PID to control temperature

  1. #21
    Boolit Master



    Join Date
    Apr 2009
    Location
    Pinehurst, NC
    Posts
    940
    Whether this becomes a sticky or not, I'm gonna copy the information given in post 10-15 and save them for future reference!

    EW

    PS: STICKY PLEASE!

  2. #22
    Boolit Buddy oldtoolsniper's Avatar
    Join Date
    Feb 2009
    Location
    Iowa
    Posts
    449
    As far as the thermo couple in my set up I just twisted it around a wire (insert red neck here) coat hanger and bent that to hold the probe in the melt not touching the pot sides or bottom. I only wish I could add some duct tape and then it would be truly well you know Red-Necked!
    “Work hard! Millions on welfare depend on it!”

  3. #23
    Boolit Master cheese1566's Avatar
    Join Date
    Dec 2008
    Location
    Black Hills, South Dakota
    Posts
    1,786
    I have thee redneck method...

    i used the same type of mount as yours, but used the base and whip from an old two way radio car antenna. it uses some duct tape to hold it to the wire whip.

    The base unit is used like a portable stand and the wire whip was bent and formed to hold the high temp probe about one inch off the bottom of the melt. Portablilty to use in my two pots. (But mine is only a temperature indicator and not a PID, I need some SSR's: hint, hint, hint!)


  4. #24
    Boolit Master



    Join Date
    Apr 2009
    Location
    Pinehurst, NC
    Posts
    940

    PID Diagram

    I found a page that explains the whole PID so well that even I can understand how the thing works.
    http://preview.tinyurl.com/PID-temp-controller

  5. #25
    Boolit Master



    Join Date
    Apr 2009
    Location
    Pinehurst, NC
    Posts
    940
    I'm thinking that you could affix the sensor tip inside a stainless steel tube and run it down inside of the lead pot (for bottom pours) to get the readings from the lead that we are using instead of the surface lead that will be fluctuating frequently from adding more lead or even the breeze flowing across the top.http://www.susanminor.org/forums/sho...e%20controller
    Attached Thumbnails Attached Thumbnails PID diagram.jpg  

  6. #26
    Boolit Master
    Elkins45's Avatar
    Join Date
    Mar 2010
    Location
    Northern KY
    Posts
    2,414
    Hey Shotgun Luckey!

    The link you provided for the PID controller is broken. Is this the correct unit? It says its for controlling an SSR. http://www.auberins.com/index.php?ma...6f31f807925e2f

  7. #27
    Boolit Buddy Shotgun Luckey's Avatar
    Join Date
    Jun 2008
    Location
    Northwood, Ohio
    Posts
    146
    Quote Originally Posted by Elkins45 View Post
    Hey Shotgun Luckey!

    The link you provided for the PID controller is broken. Is this the correct unit? It says its for controlling an SSR. http://www.auberins.com/index.php?ma...6f31f807925e2f

    That looks like the controller I used.
    Shotgun Luckey
    SASS #42629
    I'm not a top Cowboy Action Shooter, so I HAVE to look good doing it.



  8. #28
    Boolit Master Texasflyboy's Avatar
    Join Date
    May 2005
    Location
    Virginia
    Posts
    779
    Mine is about 1/2" off the bottom of the pot. Here is how I rigged my thermocouple in my big pot:







    The thermocouple just passes though a hole I drilled in some flat stock. I drilled the hole undersize and twirled sandpaper on a split stick inside the hole and gradually opened it up to a slip fit. It hasn't moved in 5 years.
    Last edited by Texasflyboy; 08-13-2010 at 09:42 AM.
    ++++++++++++++++++++++++++++

    http://www.hensleygibbs.com

    ++++++++++++++++++++++++++++

  9. #29
    Boolit Master Texasflyboy's Avatar
    Join Date
    May 2005
    Location
    Virginia
    Posts
    779
    Quote Originally Posted by Shotgun Luckey View Post
    That looks like the controller I used.

    When and if mine breaks that's the one I am going to use as a replacement. I may not wait for it to break at only $44.00.




    ++++++++++++++++++++++++++++

    http://www.hensleygibbs.com

    ++++++++++++++++++++++++++++

  10. #30
    Boolit Buddy
    Join Date
    Sep 2010
    Location
    Atlanta-ish
    Posts
    363
    This is great stuff but I have one question. Does the parts list change if I have a 220V pot?

    TIA,

    Chief

  11. #31
    Boolit Man
    Join Date
    Nov 2007
    Location
    Nebraska Panhandle
    Posts
    90
    The voltage rating for PID and SSR listed are OK for 220V.

  12. #32
    Boolit Bub
    Join Date
    Jan 2010
    Location
    Northwest IN
    Posts
    60
    How do the PID's take to changes in temp for other substances?

    My wife does candle making, and I'd love to use the same PID setup to control the melted wax at 130-200 degrees in a Presto pot and lead in my bottom pour.

    Will it work, or does it mess up the logic side of things?

  13. #33
    Boolit Mold
    Join Date
    Apr 2010
    Posts
    24
    Quote Originally Posted by wingnut49b View Post
    How do the PID's take to changes in temp for other substances?

    My wife does candle making, and I'd love to use the same PID setup to control the melted wax at 130-200 degrees in a Presto pot and lead in my bottom pour.

    Will it work, or does it mess up the logic side of things?
    I was thinking about useing a PID for more than one purpose the other day and wondering as well. Is there some kinda of recallable memory that you can use, for example, recall #1 is the lead pot and recall #2 is the candle wax.

  14. #34
    Boolit Bub kitsap's Avatar
    Join Date
    Nov 2010
    Location
    Western Washington State
    Posts
    59
    Quote Originally Posted by RedneckAlbertan View Post
    I was thinking about useing a PID for more than one purpose the other day and wondering as well. Is there some kinda of recallable memory that you can use, for example, recall #1 is the lead pot and recall #2 is the candle wax.
    I recently finished putting one together using the Auber controller. There is no setting recall that I can find. I move mine between a couple of different lead pots. Moving the full controller system from one material function to another would not be a very difficult task. Clean off the thermocouple probe and run the auto tune function when the new material comes up to temperature. The auto tune function only takes a few minutes.

    You want to be cautious using two thermostats in series. Be sure the one on the Presto cooker is set to full high value.

    Doug
    Last edited by kitsap; 12-10-2010 at 02:28 AM.

  15. #35
    Boolit Bub
    Join Date
    Jan 2010
    Location
    Northwest IN
    Posts
    60
    Thats about the way I was hoping it worked. I think I'll have to do it.

    Has anyone used the larger 'project box' on auber's site for this, or is there a better box to make this all look nice?

  16. #36
    Banned
    Join Date
    Nov 2010
    Location
    Casa Grande, AZ
    Posts
    5,526
    I you were going to be using the unit for say candle making and for your melting pot I would suggest having a separate thermocouple that you used only for the candle making venture. I would set it up so that the thermocouples could be unplugged or just bite the bullet and have two separate systems.

  17. #37
    Banned
    Join Date
    Nov 2010
    Location
    Casa Grande, AZ
    Posts
    5,526
    After reading this thread I ordered my thermocouple,SSR, and PID and will set these up to control my sizer heater temperature.

  18. #38
    Banned
    Join Date
    Nov 2010
    Location
    Casa Grande, AZ
    Posts
    5,526
    I do have a question. I ordered a thermocouple that is a type K and it has two terminals. The picture that I found on wiring is showing a three terminal connection. Can anyone help me on this?
    Last edited by 6bg6ga; 06-03-2012 at 06:59 AM.

  19. #39
    Boolit Buddy
    Lee W's Avatar
    Join Date
    Mar 2005
    Location
    Upstate NY
    Posts
    290
    6bg6ga,
    You will see in the other examples of connecting the unit, it does show a thermocouple connection. The diagram is a "V" with a dot at the point and "TC" written near it.
    Do not forget to program the unit to read a "TC" and you should be goo to go.

  20. #40
    Banned
    Join Date
    Nov 2010
    Location
    Casa Grande, AZ
    Posts
    5,526
    So I just connect between 4+5 with the thermocouple? I don't put a jumper between 3+4?

    I ordered a WRNK-191 thermocouple that is 6" long. I assume this will work?

Page 2 of 10 FirstFirst 12345678910 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check