    PID Question

    I have collected most of the components to put together a control for an electric ladel casting pot. 50 - 60 lbs. of alloy.
    My intent is to use 2-240 volt elements for quicker heat up. At a set temp. 1 element would drop off & the second 1 would maintain casting temp."k" thermocouple & ssr's will be used.
    This is the control I am looking at to get the job done https://www.omega.ca/pptst_eng/CNPT_SERIES.html. 3 dc pulsed outputs.
    The third out put would be used as a fail safe in case of a runaway.
    My question is:will this controller do what I am want or is there something else out there?

    I this is a little confusing to you,please forgive me,I have no experience with pid's.
    Any suggestions welcome.
    Thnx Lots
    Bob

  2. #2
    Boolit Master Retumbo's Avatar
    Join Date
    Nov 2014
    Location
    Ontario
    Posts
    743
    I think you are over thinking this.

  3. #3
    Boolit Mold
    Join Date
    Jan 2009
    Location
    Saskatchewan Canada
    Posts
    15
    Quote Originally Posted by Retumbo View Post
    I think you are over thinking this.
    I know this is far more complicated than I need for simple casting purposes, but I am looking to learn more about pid's and what can be done with them.
    IF this works out,I would try incorporating it into a process we are working on at the shop.
    Hopefully a call to the Omega tech. staff will help.
    Thnx Lots
    Bob
    "Ridin' For The Brand"

  4. #4
    Moderator Emeritus


    JonB_in_Glencoe's Avatar
    Join Date
    Mar 2010
    Location
    Land of 10,000 Lakes
    Posts
    15,832
    I'm not sure how much the Omega PID is? but it seems two cheap PID systems would work...just set one at a lower temp and be sure the second one "learns" while both units are on...and including, until the first one cuts out.
    ~~~~~~~~~~~~~~
    “If someone has a gun and is trying to kill you, it would be reasonable to shoot back with your own gun.”
    ― The Dalai Lama, Seattle Times, May 2001

  5. #5
    Boolit Mold
    Join Date
    Jan 2009
    Location
    Saskatchewan Canada
    Posts
    15
    BeeMan
    I thought the above control might work because it has dual set points & three outputs.
    I downloaded the manual for it but at this point on my learning curve,most of it went over my head.
    What control configuration would be needed to do what I want to do?
    Thnx Lots
    Bob
    "Ridin' For The Brand"

  6. #6
    Boolit Master
    lwknight's Avatar
    Join Date
    Nov 2009
    Location
    Fort Worth, Texas where the west begins
    Posts
    3,416
    I used the low temp alarm circuit for high power heating. You can set the alarm to whatever you want completely independent of the regular temp control. Also I do not trust the SSRs for heavy loads. You can use a 24volt transformer and 30 or 40 amp contactors.
    Sent from my PC with a keyboard and camera on it with internet too.
    Melting Stuff is FUN!
    Shooting stuff is even funner

    L W Knight

  7. #7
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,700
    you are over complicating the entire process.

    I would use a inexpensive PID and just a single SSR
    With a SSR your not gonna get a runaway situation as 99% of the time they fail to the off position.
    Get a 40 amp SSR and your golden. With that amperage, I would use a heatsink for sure.

  8. #8
    Boolit Grand Master popper's Avatar
    Join Date
    Jun 2011
    Posts
    10,572
    For your purpose a pid is used to get the temp to the set point as fast as the available heat will allow. A single controller is fine with as many elements as you want. SSR can fail open or close so if unattended, some alarm is needed.
    Last edited by popper; 10-10-2017 at 09:40 AM.
    Whatever!

  9. #9
    Boolit Mold
    Join Date
    Jan 2009
    Location
    Saskatchewan Canada
    Posts
    15
    Thank You for your help.
    I will try to talk with Omega today & see what they have to say.
    I have 65amp ssr's.
    Element size is also a concern.
    I realize this is overly complicated for casting purposes,but looking at adapting this to other process's as well.
    Again Thnx Lots
    Bob
    "Ridin' For The Brand"

  10. #10
    Boolit Master Handloader109's Avatar
    Join Date
    Jan 2014
    Location
    NW Arkansas
    Posts
    2,505
    Makes really no sense to put two bands in and try to control separately. I understand what you are trying to do, but for this application it most probably won't work. Run two off of the same controller if you want, sizing properly the SSR and then once up to temp, both will cycle. If it learns properly, there really won't be any savings with both coming on, they'll just cycle shorter times.

  11. #11
    Boolit Master
    lwknight's Avatar
    Join Date
    Nov 2009
    Location
    Fort Worth, Texas where the west begins
    Posts
    3,416
    Quote Originally Posted by BeeMan View Post
    LWKnight,

    Nicely done on sorting out a way to use the alarm. I have not used that Omega controller, so was not sure if it could do this. As far as SSRs go, just up size them so they are overrated and run cool even without a heat sink. The zero crossing feature vs a contactor makes them more reliable in the long haul and you don't need to limit the relevant PID parameter to conserve contact life. Without this constraint SSRs allow the PID setup to shorten on on off times, which in turn should help heater life because the element swings less between max (on) and min (off) temperatures.

    BeeMan
    I'm not sure about the Omega controller but anything that has a switch can be connected to a relay circuit. I plan to set up dual soloniod valve for the smelting pot. On low temp alarm , it will fire full power then drop to low till temperature setting reached then shut off to pilot mode.
    If I ever actually get it into 3D I simply must post pictures so I won't need the 1000 words.

    I opted for actual contactors for the electric pots because ( maybe its just me) I never really had much faith in SSRs You can get 40 amp contacts for about $7.00 per each and around the same for a 24volt transformer. This way the controller switch only carries low voltage and ultra low amperage. Contacts can last for years in an A/C unit so I think you would never wear one out casting.
    Sent from my PC with a keyboard and camera on it with internet too.
    Melting Stuff is FUN!
    Shooting stuff is even funner

    L W Knight

  12. #12
    Boolit Mold
    Join Date
    Jan 2009
    Location
    Saskatchewan Canada
    Posts
    15
    I finally got a chance to talk with the tech. people at Omega. Great people.
    After a long(and some what confusing for him)chat,he figures the above control will work by configuring the alarms and output setting.He did say that this will take some time trying various combinations.
    I placed the order,along with a few other items.
    If it doesn't work out,at least I will end up with a(albeit,very expensive)PID for the new pot.
    THNX LOTS
    Bob
    "Ridin' For The Brand"

  13. #13
    Boolit Master

    Join Date
    Mar 2005
    Location
    Peace River, Alberta
    Posts
    2,114
    You are overthinking.
    In fact a PID set to use the PID function is using a sledgehammer to kill a fly.
    I have a cheap ($12) PID set as a on/off thermostat. The Temp drops 1/2of a degree, the pot element heats.
    The temp goes 1/2 of a degree over, the electricity shuts off to the pot element.
    Under target temperature the pot element gets full 110 .
    It works just as well as with the unit set to the PID function.
    Go now and pour yourself a hot one...

  14. #14
    ADMIN



    HATCH's Avatar
    Join Date
    Sep 2008
    Location
    Lexington, SC
    Posts
    6,700
    It all depends on how critical you want your temp to be.
    A quality made PID will compensate for temperature overshooting.
    Basically when you kill the power to the heater yet the temp still increases.

    But for the most part of you just want to know the exact temp and have it operate just like the factory mechanical thermostat did, then setting it for just on/off operation will accomplish that goal.


    Sent from my iPhone using Tapatalk
    Don't like being hammered by the Cast Boolits Staff, then don't be a nail.
    The rules are simple to follow.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check