    DUAL Thermocouple for PID controlled convection oven?

    Anyone aware of a way to hook up a dual thermocouple, maybe one at the top and one at the bottom and it average the temps?

    Since having one TC in an oven is just going to measure that one spot, wouldn't having 2 that average give you a more accurate temperature over the entire oven?

    Just curious if this has been done or am I thinking wrong?

  2. #2
    Boolit Buddy
    Join Date
    Dec 2015
    Posts
    134
    No need.
    Unless you have element on top you want to use a separate PID on.


    Sent from my iPhone using Tapatalk Pro

  3. #3
    Boolit Buddy rototerrier's Avatar
    Join Date
    Mar 2011
    Posts
    456
    Correct. I have a dual element and find the temp on the top rack to always be higher than the bottom, even with convection. I can only use the top rack to be sure I'm at the right temp. I suppose a dual pid would work.

  4. #4
    Boolit Master

    Mike W1's Avatar
    Join Date
    Nov 2008
    Location
    Rural Sumner, IA
    Posts
    1,317
    The PID's I've seen only have one input for a TC so you'd need 2 PID's. Some genius might be able to come up with a way to average the temperature but I'm not a genius. Suppose there's probably an industrial version that could do it but it'd likely be out of our price range for casting.
    Mike

    Benefactor Member NRA
    Life Member Iowa Firearms Coalition
    US Army Vet

    There are two ways to conquer and enslave a nation.
    One is by the sword. The other is by debt.”
    John Adams 1826

  5. #5
    Boolit Master
    Ausglock's Avatar
    Join Date
    May 2010
    Location
    NSW North Coast, Australia
    Posts
    3,162
    If the airflow in the oven is adequate, only 1 probe is needed and placed in the centre of the oven.
    Mine is under the centre of the middle rack.
    Hooroo.
    Regards, Trevor.
    Australia

  6. #6
    Boolit Master dikman's Avatar
    Join Date
    May 2013
    Location
    Sth Oz - A Land Downunder
    Posts
    2,087
    Interesting idea, but I don't think it would work too well. I reckon you'd still end up with hot spots at the top of the oven. Effective circulation is the only way to keep a constant even temp, but using a small oven, with the elements close to the top and bottom, makes it difficult. If you can boost the air circulation that might help?

  7. #7
    Boolit Buddy
    LabGuy's Avatar
    Join Date
    Sep 2010
    Location
    Tallahassee Florida
    Posts
    348
    Money and time would be better spent on verifying circulation.

  8. #8
    Boolit Master

    Mike W1's Avatar
    Join Date
    Nov 2008
    Location
    Rural Sumner, IA
    Posts
    1,317
    Looking thru some PID manuals tonight and noticed something. Have no idea if it would work for this but there's an illustration on page 7 of Auber's manual showing 2 TC's hooked up to maintain a temperature difference. Their tech staff is pretty sharp so you might want to get hold of them and tell them what you have in mind. Bet they'd have an answer one way or the other if it's feasible.
    Mike

    Benefactor Member NRA
    Life Member Iowa Firearms Coalition
    US Army Vet

    There are two ways to conquer and enslave a nation.
    One is by the sword. The other is by debt.”
    John Adams 1826

  9. #9
    Boolit Mold
    Join Date
    Mar 2013
    Posts
    4
    An average temperature can be read by wiring two or more thermocouples in parallel into the same input of your PID controller. You won't know individual temperatures this way, just the average.

    http://www.dugantech.com/Product_Gro...asurements.pdf

    Whether it is needed or not is debatable.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check