    Need home electrical advice.

    Just left my master bedroom. When I switched off the overhead light, it flickered a bit at first. Curious I switched it back on, but now it won't go off. Not making any sparks, smoke or anything else. I opened the breaker and closed it again, same thing.

    My back is a mess, and I'm not the best at electrical. What is the more likely source of trouble, the switch or the fixture? Hardware store is closed here now. I did back out the bulbs, but the fixture might still be hot. What's the risk going to bed tonight?
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  2. #2
    Boolit Master Handloader109's Avatar
    Join Date
    Jan 2014
    Location
    NW Arkansas
    Posts
    2,533
    Bad switch. If switch worked power to light would go off.
    If older home, does it have aluminum wiring? Don't use back stab, put wiring under screws. Spend more than $2 for your next switch, get quality.

  3. #3
    Boolit Master
    Join Date
    Dec 2011
    Location
    Southwest MO.
    Posts
    1,886
    The problem probably lies in your switch.
    If you back the lamps out I can't see any danger.
    Some people live and learn but I mostly just live

  4. #4
    Boolit Buddy

    Riverpigusmc's Avatar
    Join Date
    Apr 2013
    Location
    North Central Florida
    Posts
    244
    Quote Originally Posted by Handloader109 View Post
    Bad switch. If switch worked power to light would go off.
    If older home, does it have aluminum wiring? Don't use back stab, put wiring under screws. Spend more than $2 for your next switch, get quality.
    ^this. Get a good Leviton switch and avoid the quik stabs in the back
    NRA Life Member
    Member Florida Carry
    Founding member/moderator COTEP

  5. #5
    Boolit Master
    Join Date
    Feb 2015
    Location
    Cass county, Michigan
    Posts
    659
    All of the above and MAKE SURE THE BREAKER IS OFF before you attempt to replace the switch.

  6. #6
    Boolit Buddy
    Join Date
    Apr 2014
    Location
    Sunny Southeast Alaska
    Posts
    204
    [QUOTE=Pipefitter;3318793]All of the above and MAKE SURE THE BREAKER IS OFF before you attempt to replace the switch.

    But that will take all the sport out of it

  7. #7
    Boolit Buddy
    Join Date
    Sep 2011
    Posts
    187
    It's just 110.

  8. #8
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Just about to test that, but don't know if my method will be safe. I plan to screw the bulbs back in till lights come on. Then, open the breaker, disconnect the switch, close the breaker to see if the lights go off.
    Last edited by wallenba; 07-20-2015 at 09:47 PM.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  9. #9
    In Remembrance
    oneokie's Avatar
    Join Date
    Oct 2007
    Location
    Jackson County, Choctaw Nation, Indian Territory
    Posts
    4,873
    Quote Originally Posted by bnelson06 View Post
    It's just 110.
    Yeah, rightttttt.
    Ever been bitten real good by 110? I have, it is not fun. Also been bitten by 440, that hurts!
    Those who fail to study history are doomed to repeat it.

    “A fear of weapons is a sign of retarded sexual and emotional maturity”. Sigmund
    Freud

  10. #10
    Boolit Buddy
    Join Date
    Sep 2011
    Posts
    187
    All the time Nolan, working in electrical panels tends to get ya use to it ........ Not a good thing

  11. #11
    Boolit Grand Master

    Join Date
    Oct 2009
    Location
    England,Ar
    Posts
    7,700
    I agree, its probably the switch. Or the connection at the switch. Removing the load (taking the bulbs out) removes most of the hazard. Changing switches is pretty easy with a few basic tools. I'm old school and do nearly everything hot. Get a flashlight and turn the breaker off, remove the old switch and go buy one like it. Its important to match the switch. Most bedrooms will be a single pole switch (2 screws + the ground), but some larger rooms will have a 3-way (3 screws + a green ground). If its a 3-way switch, take note which wire is on the black or gold screw and the green screw. The other 2 wires can go on either of the remaining screws.

  12. #12
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Disconnected the switch with the lights on. Opened the breaker. Lights are out. Logic says switch. Get one tomorrow.

    I have a healthy fear of home electrical. When I was seven, my mother found me on the kitchen floor with a butter knife in my hand. Yep... the toast was burning because it got stuck when it tried to pop up. "I'd done that a lot of times I told her, that never happened before". Didn't even blow a fuse. I don't think they had GFI's in 1959.I was banned from the kitchen for many years.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  13. #13
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Quote Originally Posted by Handloader109 View Post
    Bad switch. If switch worked power to light would go off.
    If older home, does it have aluminum wiring? Don't use back stab, put wiring under screws. Spend more than $2 for your next switch, get quality.
    Yes, house was built in 1952, same age as me, 63.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  14. #14
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Quote Originally Posted by lightman View Post
    I agree, its probably the switch. Or the connection at the switch. Removing the load (taking the bulbs out) removes most of the hazard. Changing switches is pretty easy with a few basic tools. I'm old school and do nearly everything hot. Get a flashlight and turn the breaker off, remove the old switch and go buy one like it. Its important to match the switch. Most bedrooms will be a single pole switch (2 screws + the ground), but some larger rooms will have a 3-way (3 screws + a green ground). If its a 3-way switch, take note which wire is on the black or gold screw and the green screw. The other 2 wires can go on either of the remaining screws.
    Things don't look right inside that box. Both (only two wires) connected to the switch are black. There is a white wire tucked away in the back. Can't see where that goes. Wires are copper.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  15. #15
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Quote Originally Posted by lightman View Post
    I agree, its probably the switch. Or the connection at the switch. Removing the load (taking the bulbs out) removes most of the hazard. Changing switches is pretty easy with a few basic tools. I'm old school and do nearly everything hot. Get a flashlight and turn the breaker off, remove the old switch and go buy one like it. Its important to match the switch. Most bedrooms will be a single pole switch (2 screws + the ground), but some larger rooms will have a 3-way (3 screws + a green ground). If its a 3-way switch, take note which wire is on the black or gold screw and the green screw. The other 2 wires can go on either of the remaining screws.
    [
    Things don't look right inside that box. Both (only two wires) wires connected to the switch are black. There is a white wire tucked away in the back. Can't see where that goes. Wires are copper.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

  16. #16
    In Remembrance
    oneokie's Avatar
    Join Date
    Oct 2007
    Location
    Jackson County, Choctaw Nation, Indian Territory
    Posts
    4,873
    Probably wired with 2 conductor wire. Outlets use 2 or 3 prong plugs?
    Switch should kill the juice to the fixture if you only have the 2 wires connected to the switch.
    Those who fail to study history are doomed to repeat it.

    “A fear of weapons is a sign of retarded sexual and emotional maturity”. Sigmund
    Freud

  17. #17
    Boolit Master Handloader109's Avatar
    Join Date
    Jan 2014
    Location
    NW Arkansas
    Posts
    2,533
    Do you have two switches that turn on the lights in the bedroom? I expect not, would be common in living room, but not in bedroom. No telling being that old. I'd rewire new switch same as old and be done with it.

  18. #18
    Boolit Master

    jcren's Avatar
    Join Date
    Nov 2014
    Location
    South, Central Ok
    Posts
    2,174
    Your switch wiring is normal, the black wire is switched and the white wires should be wire-nutted together. Use previously discussed caution and snug wire screws firmly and give her a shot. And yes, 440 3-phase bites much worse than 110!
    "In God we trust, in all others, check the manual!"

  19. #19
    Moderator Emeritus

    MaryB's Avatar
    Join Date
    Jun 2013
    Location
    SW Minnesota
    Posts
    10,321
    I was working on a VCR with the power supply exposed on one side. I laid on hand over the fuse, the other over chassis ground and started to flip it over. Got halfway and realized I was across the line... finished flipping it then cussed a bit. Part of working on electronics, getting zapped. 110 doesn't even bother me. Mt dad was an electrician and his fingers were so callused and used to it he would lick his finger tips and brush them across exposed wires to see if the are live.

    I agree, bad switch, pretty common failure and very easy to replace. 2 wires, can't put them on backwards(doesn't matter which terminals they go on as long as they are opposite contacts). I would just swap it with power on but getting zapped doesn't bother me.

    Quote Originally Posted by oneokie View Post
    Yeah, rightttttt.
    Ever been bitten real good by 110? I have, it is not fun. Also been bitten by 440, that hurts!

  20. #20
    Boolit Master
    wallenba's Avatar
    Join Date
    May 2009
    Location
    S. E. Michigan
    Posts
    2,695
    Quote Originally Posted by oneokie View Post
    Probably wired with 2 conductor wire. Outlets use 2 or 3 prong plugs?
    Switch should kill the juice to the fixture if you only have the 2 wires connected to the switch.
    The outlets all have 3 prong receptacles. That doesn't mean much. The house passed inspection in the bath and kitchen when I bought it. I hired an electrician when we did the kitchen. He showed me that the GFI's were not wired. They redid the bath too.

    Handloader109, just the one switch. Going to rewire it as before. Thanks for holding my hand here guys.
    Dutch

    "The future ain't what it used to be".
    -Yogi Berra.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Abbreviations used in Reloading

BP Bronze Point IMR Improved Military Rifle PTD Pointed
BR Bench Rest M Magnum RN Round Nose
BT Boat Tail PL Power-Lokt SP Soft Point
C Compressed Charge PR Primer SPCL Soft Point "Core-Lokt"
HP Hollow Point PSPCL Pointed Soft Point "Core Lokt" C.O.L. Cartridge Overall Length
PSP Pointed Soft Point Spz Spitzer Point SBT Spitzer Boat Tail
LRN Lead Round Nose LWC Lead Wad Cutter LSWC Lead Semi Wad Cutter
GC Gas Check