Originally Posted by
sharps4590
Ok, first off 10 amp breakers either are, or, have been available but they are special order and it would be HIGHLY unusual for any electrician to install them unless specifically required for a particular piece of equipment and usually something like that is taken care of at the equipment by a fused disconnect where the fuses are the protection for the equipment and the breaker is the protection for the wiring. As has been pointed out 15 and 20 amp are the most common, 120 volt breaker sizes IN RESIDENTIAL application. The "interrupting current" of residential breakers is 10,000 AIC, "Amps Interrupting Current". I have seen that abbreviated on some residential breakers as "10K AIC" and have a had a lot of customers over the years tell me they have "10 amp breakers" in their panels when they don't. There should be a number 15 or 20 on the either the breaker body or the breaker handle specifying what the amperage is of the breaker. After, as I said, 42 years of doing this for a living I really doubt you have 10 amp breakers. If you do, yours is the first I have ever heard of and I have never seen it.
I have known of some old time electricians who would put 15 amp breakers on #12 wire and there's nothing wrong with that except that the safe capacity of the wire is not available. As per NEC, in residential applications, #14 wire is good for 15 amps, #12 is good for 20 amps and #10 good for 30 amps, #8 for 40 and #6 for 50 or 60, depending. If those are exceeded one is in violation. After that Section 310-16 is the "go to" article in the NEC for wire ampacities as the type of insulation has a bearing on the capacity of the wire as well as wire size.
In nearly all commercial applications I've worked on the AIC is specified to be 20K, AIC. I don't remember what it is as voltages got higher as in 277/480 and the old 230/460.